What is a generator full load rejection test?
---------------------------------------------------------------------
id...@mhs-tva.attmail.com <========= Internet Address (work)
rw...@ra.msstate.edu <=============== Internet Address (school)
rp...@chattanooga.net <===== Internet Address (home)
---------------------------------------------
Few machines (>1000 MWe) can do this. Some facilities may refer to near
full load rejection as a full load rejection, e.g. a nuclear plant
may continue to carry in-house loads after a load rejection.
A variation on this is the test to assure the boiler/nuclear reactor
system can continue to operate after a load rejection. This requires
some means of dumping the steam being generated to the condenser or the
atmosphere, and quickly ramping power down (heat generation / steam
flow), until the turbine can be restored.
Hope that helps. BTW, these tests are fun to watch! Bang, woooosh,
roar, etc. <grin> "MORE POWER"
>A full load rejection test usually refers to the capability of a turbine
>generator set to continue to operate, when the generator output breakers
>have been opened or excitation is lost. This results in the machine
>attempting to overspeed (no load after the breakers open) and the inlet
>and intercept valves (if any) having to immediately modulate to a near
>closed or closed position.
Not for nuclear plants. See below.
>Few machines (>1000 MWe) can do this. Some facilities may refer to near
>full load rejection as a full load rejection, e.g. a nuclear plant
>may continue to carry in-house loads after a load rejection.
Not quite true. GE BWR's for sure, and I'm fairly certain for Western
designed PWRs, can withstand a full load rejection. In this case, this
means that no safety paramenters are exceeded, but the turbine-generator
and the reactor both trip.
>Hope that helps. BTW, these tests are fun to watch! Bang, woooosh,
>roar, etc. <grin> "MORE POWER"
Agreed that these are fun to watch since the main turbine trips and on a
1000+ MW turbine, those stop valves closing are heard/felt throughout
the plant.
Bill Kohn
Oak Ridge, TN
Thanks!
--
Marty Bernard *Making EVs Current*
National Station Car Association
hppt://www.stncar.com
stn...@ix.netcom.com
>What is a generator full load rejection test?
The generator load is increased to 100%, then the unit circuit breaker
is opened. This typically is used to check over-speed of the unit, and
proper shutdown. It can be very impressive if you are doing a full
load rejection test on an entire powerhouse. It can put barges into a
parking lot.
: >Hope that helps. BTW, these tests are fun to watch! Bang, woooosh,
: >roar, etc. <grin> "MORE POWER"
: Agreed that these are fun to watch since the main turbine trips and on a
: 1000+ MW turbine, those stop valves closing are heard/felt throughout
: the plant.
: Bill Kohn
: Oak Ridge, TN
I've been present for these kinds of tests on hydro generators and
diesel-driven generators.As long as everything goes right, they are
indeed fun to watch. Full load rejection (and its companion load
acceptance or block loading) can really make a 5MW (6500HP) diesel engine
rock (or grunt as the case may be).
For a real good time though, I think full load rejection on a >100MW
turbine in a hydro generating plant is a strong contender. Noise. Dust
rising/falling everywhere. Huge sigh of relief that you're not suddenly
being transported downstream by tons of water. Amazement that tons of
concrete can shake without falling apart. (New construction only - I
don't know if this test is done on old & refurbished units. Don't think
I'd want to be in the plant at the time.)
9800, Metcalf Ave., Overland Park, KS 66212-2215
Tel: 913 341-1300
Fax: 913 967-1904
The functional test is usually required on new units as a condition of
acceptance during the start-up phase.
--
-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-
Sent via ExpressNet/SMTP(tm), Internet Gateway of the Gods!
ExpressNet/SMTP (c)1994-95 Delphic Software, Inc.
-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-
Depending on your droop setting, the governor actually will regulate the turbine
speed ABOVE the rated speed, assuming no subsequent adjustment to the governor.
E.g. if your droop setting is 4%, the regulated STEADY STATE speed is 104% of the
rated speed after full load rejection. The governor and valves are supposed to act
quickly enough to prevent the overshoot to trigger the overspeed trip (usually
110-111% of rated speed) of the turbine.
The system I used to work is a ~1200MW system with a tie line to a ~3000MW system.
We were commissioning a 350MW coal-fired steam unit. We could not take the risk of
a full load rejection so we did a 30% and 60% rejection and (dangerously)
extrapolate the test result. And we boosted the system frequency to 50.50Hz (50Hz
system) before the test.