Chevron Pascagoula Fire: Importance of Flange QA/QC - Loose Flange Bolts at PSV
A crude unit at Chevron's Pascagoula refinery experienced a big & costly fire back in August. Some of you have probably already seen photos of this fire (attached). The official investigation report has not yet been issued, but the likely scenario of events leading up to this fire has been informally reported as follows:
A 4 X 6" or 6 X 8" PSV (size
depends on who you talk to) was removed for routine servicing at last TA but
when it was reinstalled, the flange bolts were not properly tightened (maybe
only hand tightened)
The PSV was not easy to access; the
loose PSV inlet flange probably leaked a small amount for quite some time, but
the small leak was not detected due to the PSV's location
Some time well after TA, the PSV
started "simmering" due to system pressures getting close to the PSV
set pressure.
The simmering of the PSV was just the
"right frequency" such that multiple of the loose stud nuts backed
off the studs and some nuts fell off completely
With missing and very loose nuts, the
flange opened up enough to cause a significant release, and the fire
pictured.
|
|
|
|
|
|
|
|
Best regards,
Sunil S. Agrawal
Engineering & Design Tecnimont ICB
Static Equipment Dept. (STEQU)