Dear All, please share your opinions

GRE pipes damaged at few location after hydrotest. Damaged location repaired. Contractor proposal is carry out test with operating pressure.
Question:
1. Is normal to test with operating pressure? Damaged GRE pipes in particular
2. Is it advisable to use such kind of fixed GRE pipe on site even after testing?

Regards

Muthukrishnan Sivaramakrishnan

unread,
May 21, 2014, 12:34:59 AM5/21/14
to material...@googlegroups.com
Dear Mr.Maedtro ,

We repeat the hydro test if the pipe is new and unused .
If the repair is done on a used pipe then we test it at operating pressure and hold it for 30 min  before using the pipe .
I advise additional lamination on repaired joints .
Regards,

S.Muthukrishnan


--
To post to this group, send email to material...@googlegroups.com
To unsubscribe from this group, send email to materials-weld...@googlegroups.com
For more options, visit this group's bolg at http://materials-welding.blogspot.com/
http://www.linkedin.com/groups/MaterialsWelding-122787?home=&gid=122787&trk=anet_ug_hm
 
The views expressed/exchnaged in this group are members personel views and meant for educational purposes only, Users must take their own decisions w.r.t. applicable code/standard/contract documents.
---
You received this message because you are subscribed to the Google Groups "Materials & Welding" group.
To unsubscribe from this group and stop receiving emails from it, send an email to materials-weld...@googlegroups.com.
For more options, visit https://groups.google.com/d/optout.

Reply all
Reply to author
Forward
0 new messages