Hydrotesting Calculation of Steel pipeline

208 views
Skip to first unread message

tejas kerzare

unread,
Apr 14, 2021, 12:45:05 AM4/14/21
to material...@googlegroups.com
Dear All,

Please can you Provide Hydrotesting calculation of the steel pipeline having pipe API 5L Grade B.
Pipe Size - 10 Inch 
Thickness -  6.4 mm
Total Length of Steel pipeline - 1000M.

Thanking You!

Alcindo Jardim

unread,
Apr 14, 2021, 10:38:01 AM4/14/21
to material...@googlegroups.com
What do you want to calculate? the isolation for the test, or the pressure for the test?
If you want the isolation I can send you an excel that calculates it. If you want the pressure it depends on the project, it may be 1,5 times the project pressure, according to the code of the project.

Alcindo O. J. Jr.



--
https://materials-welding.blogspot.com/
https://www.linkedin.com/groups/122787
---
You received this message because you are subscribed to the Google Groups "Materials & Welding" group.
To unsubscribe from this group and stop receiving emails from it, send an email to materials-weld...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/materials-welding/CAPv03FtvoiimrgkJqacUt3MM-e8yQ4W-tPc7r%3D_3oAYFMb3mhw%40mail.gmail.com.

Vinay Thattey

unread,
Apr 14, 2021, 10:56:17 AM4/14/21
to material...@googlegroups.com
Dear Tejas ;

it's a schedule 20 pipeline . But you need to know about design pressure OR maximum allowable operating pressure  and also operating temp
erature 
Generally, (gas )pipelines are hydrotested by filling the test section of pipe with water and pumping the pressure up to a value that is higher than maximum allowable operating pressure (MAOP) and holding the pressure for a period of four to eight hours.

--

tejas kerzare

unread,
Apr 16, 2021, 8:16:12 AM4/16/21
to material...@googlegroups.com
Dear Sir,

The Operating pressure is 19 bar & the Max Allowable Pressure is 32 Bar &with Operating Temp is 32-degree Celcius. 

I need the Standard Deadweight testing calculations formula with the Procedure which is used in CGD.







Alcindo Jardim

unread,
Apr 16, 2021, 8:34:41 AM4/16/21
to material...@googlegroups.com
32 x 1,5 = 48 bar is the test pressure
Alcindo O. J. Jr.
21 96676-1511



Reply all
Reply to author
Forward
0 new messages