Hi all,
yes, I agree to both latest comments ... I was just writing, but I am actually a bit slower in writing than Simo.
As mentioned during the Webex session, it would be very valuable to get a more detailed
understanding about the applied systems. This would account not
only for the TGA system, but also to the different variants for small scale
testing like the cone tests (but also all other systems).
- In particular it would be good to get an understanding about the specs (e.g.
accuracy, range, peak-to-peak noise, …) of the load balance in TGA and
Cone/FPA/Capa. E.g. for cone, I expect, that an accuracy of 0.1g is
challenging in terms of accuracy.
- Similar as for the TGA measurements, the cone temperature curve would be of
interest; especially when comparing different systems. I am not sure, if there
is some similar measurements for the FPA lamps!?
- Temperature profile in the exaust duct
- For the backside temperature measurements it would be of interest how the
contact was accomplished during the tests.
- And it would be good to add any special visual observations during the tests.
Further for the reporting I would like to see the unfiltered data (for TGA and
Cone) as well. This would give some additional insight to the fluctuations of
the measurements. E.g. that means, that it would be good to have the filtered and
unfiltered MLR data for the cone measurements in addition to the HRR curves as
well.
And I agree to have shorter names for the plotting. In the beginning I was a bit
confused by the non-disclosed laboratory names in the report, but actually
think, that it was a good decision, so that everyone could get a non biased
first overview.
Best Regards
Fabian