Hi,
We chose a 'dumb' system specifically because we have Loxone and intended to perform any control through that. It was quite tricky to find something affordable that could be interfaced with Loxone but ended up with a S&P (Unelvent) Domeo 210. They do larger models if your house isn't as small as ours.
Comms are via Modus and this seemed a bit temperamental to begin but think that was a wiring issue as now works fine. Fortunately you can change the address and other settings of the device to suit your Modbus implementation.
We have numerous points of control:
- Scaler block which sets demand according to humidity.
- Scaler block which sets demand according to air quality (we have $5 homemade MQ135 AQ sensors in a couple of rooms - works well).
- Demand boost on a timer when someone is in the WC (PIR sensor).
- Demand boost on a timer when someone takes a shower (detected by sudden jump in bathroom humidity but it has been suggested to put temperature sensor on the hot water shower manifold to detect flow there).
- Demand boost when the kitchen hood is on (we have a recirculator as the house is airtight). Ikea model I hacked to put a relay inside so Loxone knows when it's fan is running.
- Put the unit on bypass (fresh air directly into the house avoiding the heat exchanger) if temperatures in/out warrant this. Mainly for summer nights to bring in colder air if the house has become a little warm in the day. It's a bit more noisy in bypass but if we are away from home have it run full bore as who cares how noisy it is when we're away ;)
- Change the airflow balance and reduce flow if a window is open somewhere.
Think that's about it.
The manufacturer sells flow restricting vents (BM2D range aimed at commercial buildings) and I would like to fit these to the extraction rooms. They are 70EUR a pop though (plus the hassle of wires and more actuators) and right now seems like a convenience we don't need. The idea is that if you restrict flow to just the room that needs demand (taking a shower for example) then the overall flow rate can be lower as the other rooms would be 'closed' and not much airflow would happen there. Maybe will add these when we fit out our attic (further bedrooms and bathroom).
HTH.
Robin