Thanks Duncan
I did some more testing. When the wires are disconnected from miniserver and the beam sensor is blocked I indeed get 24V (and 0 when unblocked) on the wires that I would connect to the miniserver so I know my wires are OK
The power supply at the gate is a long distance from my cabinet (probably close to 100m of cable)
When I measure the voltage from the - on the wire to the - on loxone it is about 0.2V difference so I was thinking that would be insignificant.
When I connect the +24 from the sensor and measure to the - which is not connected to the miniserver I still get the 24V
As soon as I connect the - to the miniserver the voltage at my input goes from 24V to 3V.
Do you think this is due to different grounds? And if so are you proposing that I connect a wire from the - of the 24V supply at the gate to the - of the 24V supply at Loxone? Just want to clarify that part.