Power meter Schneider iEM3250 Modbus

229 views
Skip to first unread message

Mantas Fabijonavičius

unread,
Dec 22, 2017, 3:07:51 PM12/22/17
to Loxone English
Hi,

Trying to connect Schneider iEM3250 electricity power meter via Modbus but no success after many trials.

I am using Loxone modbus extension setted up at BAUD-19200, parity-none, stop bits - 1.

I want to read active power in kW so I have added analog sensor, but it shows zero after all..

Maybe someone have experience in this?

Thanks in advance

Regards

Mantas

Viktor Granbom

unread,
Dec 23, 2017, 12:50:00 AM12/23/17
to loxone-...@googlegroups.com
Hi, i have a iEM3155 working with the same settings as you. Every adress in their manual is 1 higher than loxone. I.e if you want to use adress 3000 in their manual you should use adress 2999 in loxone.

I use adress 3059 for active power (command 3 - Read holding register) and 32-bit floating point.

/Viktor

Mantas Fabijonavičius

unread,
Dec 24, 2017, 8:24:47 AM12/24/17
to Loxone English
Hi,

Thanks a lot for information, I will run a test soon, as I understood if I want to measure active power it should look like this? (Or I need to tick "Combine 2 registers"?)

Viktor Granbom

unread,
Dec 25, 2017, 1:14:43 AM12/25/17
to Loxone English
I think have combined two registers (but you should get data anyway).

Mantas Fabijonavičius

unread,
Dec 26, 2017, 4:33:36 PM12/26/17
to Loxone English
It works, thanks a lot for helping!

Regards,

Mantas