Hello,
So I came on here a few months back asking about Underfloor Heating Controls. So getting in a bit of a muddle of how best to run the Underfloor System.
I have effectively 16 zones/rooms that have a Loxone Air Temperature/Humidity Sensor in each. Each zone has a separate Manifold Valve (On/Off) installed on a common underfloor heating manifold.
The manifold can be controlled to a temperature using a 4-way mixing valve from the boiler, I utilise a 1-wire temperature sensor clamped to the copper pipe on the mixing controller underfloor outlet. This valve controls the temperature to a setpoint, using a Mixing Controller and works well, i.e. the mixing controller works perfect, thus allowing you to tell it a temperature from boiler and it will control to that.
There is a separate pump for the underfloor system after the mixing controller, solely for the underfloor heating pipework.
In the next couple of weeks I will have a 1-wire temperature sensor installed outside, so I can measure external temperature.
I am currently using Intelligent Room Controllers for each room, central Intelligent Temperature Controller(Mixing Demand Temperature) and Climate Controller to turn Pump & Boiler on.
At the moment the boiler seems to be running a lot as I am running a lower
temperature on the underfloor system due to the Intelligent Temperature
Controller running at 25-33 DegC based on room demand. I manually had it
running at 45 DegC, before I started using the temperature controller demand
and this seemed to heat the rooms up quicker, but I didn’t think this was most
efficient.
Does anyone have any experience of running underfloor heating systems and the best method of control, including setup within loxone. I understand from other folk that you don’t run it like a radiator system and effectively should be constantly running a temperature in the underfloor screed, however I do not want to run it hot all the time. I just don’t know here. Its all working, but just not very efficient at all.
Any help is greatly appreciated.
Thanks
Mike
on a related note, weather compensation requires not only the external temperature, but also the wind-chill effect (perceived temperature in the loxone weather service) as the resulting air changes in windy weather significantly increase heat loss.
mperature, but also the wind-chill effect (perceived temperature in the loxone weather service) as the resulting air changes in windy weather significantly increase heat loss.That's an interesting point. Presumably not relevant in an airtight house with controlled ventilation (not the case for all but a very few UK houses).Actually, I think it should apply even then. If you think about it then windchill is basically blasting a surface with cold air and sucking heat away faster than if it were just sat there without the wind.
Allegedly it's more effective to not let the temperature drop too far and then have to heat up a lot when it's in use. This is allegedly more relevant with UFH when the heating medium (your floor) is very slow to respond. I say, 'allegedly' because just read an article where they say British Gas recommend only heating rooms based on use.
If you have a well insulated house then look at Duncan's "european" approach above. That's how my heating operates (using Viessmann's own weather compensation system).
On Tuesday, 15 January 2019 15:00:25 UTC, Simon Still wrote:If you have a well insulated house then look at Duncan's "european" approach above. That's how my heating operates (using Viessmann's own weather compensation system).I'd add that Duncan doesn't seem to think this strategy works but I'm very happy with it.
have you tried to use a custom mode set to lowered temperature (say 1-2deg lower than comfort) and triggered by sunshine flag to turn down your thermostats from the normal comfort temperature ? it might give you better overall control with a degree of automation.
I'd add that Duncan doesn't seem to think this strategy works but I'm very happy with it.I can tell you that as described that wouldn't work for us because when it's sunny we get a massive amount of heat from solar gain and don't need the heating at all.And to a lesser extent, if we have friends over for dinner the added number of bodies also has an impact.