What have we ended up with, or what would I deploy if starting from scratch? ;)
**Sorry, long story...
Originally we had 400W of Meanwell PSUs spread as 3 x 100W for lighting and 1 x 100W for Loxone, Modbus relays and the like. These were DR100-24 units. I have them for sale (lightly used) if anyone is interested ;)
Then I discovered the EldoLED dimmers we have didn't like a PSU that wasn't grounded so switched them out for 4 x NDR-120 units.
Given the decision to go to the NDR range form factor added 2 x DR-RDN20 units to connected the 4 x NDR-120 in a redundant manner.
This worked great for a while but then the issue of our unreliable mains electrical supply came into focus (we live in the French countryside and the supply is very susceptible to storm activity) so added a DR-UPS40.
Thing with this setup is that the DR-UPS40 unit doesn't charge it's SLA battery unless the input voltage is high enough. For 24v SLA battery one should charge to at least 28.4 it seems. I had hoped the DR-UPS40 would have a built in DC-DC boost for that, but it isn't designed that way, and TBH, no wonder given how economical it is. I did look at other 24v UPS systems but they were all much more expensive and also wanted to work with what we already had. TBH, having separate DC-DC units later (read below) makes the the system more modular so think I prefer that.
So to get the batteries to charge, the DC bus between the DR-RDN20 units and DR-UPS40 has to be adjusted to 28.4v. No problem as there are pots on the NDR series PSUs that allow that.
Problem is then that Loxone (and I later discovered, our 24v lights - not the dimmers, they can handle higher voltage just fine, but the LED emitters themselves) don't like 28.4v input so I bought a Meanwell DDR-60G-24 to regulate (it's a boost/buck unit) the Loxone, Modbus supply to 24v and some cheap Chinese DC-DC regulators for lighting (200W for 2-3EUR each!) as the dimmers are obviously redundant (if one fails other lights are still available). I also added a cheap Chinese DC-DC boost converter to get a 29v supply from the DC bus and connected that to an ABB DR/S4.1 KNX choke (replacing our original MDT KNX PSU) so that the KNX devices can also run from the battery.
All this works great. Phew!
I used 2 x 7.2Ah 12v SLA batteries BTW. SLA batteries are only supposed to be discharged to half capacity but even with that, these will run our Miniserver and a few lights for several hours. I will also add more cheap DC-DC converters later to run a Raspberry Pi and network router from the battery. Stopping these things rebooting during short power outages is more important to me than having really long term battery power.
I should also note that the DR-UPS40 has dry contacts for DC OK, Battery Discharge & Battery Fail but... the 'Battery Discharge' only comes on when it's pulling more than 2A from the battery. I had to turn on a lot of lights to get that to come on! Because of this I've utilised the dry contacts on the DR-RDN20 units to detect power outage as these are triggered as soon as the PSU on the associated input fails (if they all fail at the same time assume mains has failed). I couldn't get the 'Battery Fail' light or dry contact to function either, although that might just be my misunderstanding of that contact - perhaps it's only meant to come on when the battery charge level is getting critically low.
This was all a bit of an evolution as you can tell! At one point I was getting a bit annoyed at having to get more hardware, especially around regulating/boosting the DC levels but TBH none of this gear is that expensive.
So yeah, in the end it really isn't that expensive (I imagine still be cheaper than equivalent 24v & KNX PSUs from Loxone!) and has a lot of redundancy and the battery backup.
All that taken into account, if I was starting again what could be done better? I'd probably change out the small Meanwell DDR-60G-24 and the various Chinese converters for 2 x DDR-240B-24 units. These are voltage regulators that do redundant current sharing so would be more reliable, but they are a bit more expensive. I should really have used a DDR-30G-24 (adjusted to it's max output of 28v) for the ABB KNX choke rather than a cheapo Chinese one I guess, but we'll see how long the cheap one holds up.
Anyhow, hope that wasn't too long winded and helps in some way.