To see if there are CRC errors:
Click on 1 wire extension in periphery window
Click on device status
Right click on the 1 wire extension in status window
Click on detailed device information Give it a few seconds and a txt file will come up with information.
You should have many packets with 0 or very few CRC errors. CRC errors are caused by having too many sensors or too long a run or noise in the lines.
It should say 0 85 Degree problems or close to zero - 85 Degree problems are caused by not having enough voltage for the sensor.
If there are excessive CRC errors the bus will stop running and the values on the Loxone will show the last value which could cause serious failures.
To get an alarm upon failure of a sensor:
Click on the sensor
Check “Display Error Output”
Check Use Validation and enter a value for Receive Timeout – This value will depend on how often you poll for temperature, I used 60 seconds
Go to Messages in periphery