Peter
What does ComCheck want for input ? Is it the U-factor / R-value of the wall including the window ? Or does it separate out the window U-factor from the wall U-factor ?
Here is how I would suggest you break up the U-factor calculation if you are using one THERM model. If you need to input a UA value, then you would multiple the U-factor of each tagged THERM section, then multiply that times the area of that type of wall, and then sum them together to get a total wall UA (if that is what you are trying to calculate). The places where you change the U-factor tags are where the isotherms become parallel. You will see that is where I separated the Window Frame / Wall U-factor from the regular Wall U-factor – you want to find the point in the cross section where the window frame is no longer affecting the heat flow / temperatures. In terms of how to break up the Window Frame from the Center of Glass, you should look at the NFRC Simulation Manual on our website – in particular look at page 6-35, which shows how far up the glass to start the Center of Glass U-factor tag.
http://windows.lbl.gov/software/NFRC/SimMan/NFRCSim6.3-2013-07-Manual.pdf
***
Robin Mitchell
Windows & Envelope Materials Group
Lawrence Berkeley National Laboratory
--
You can view the THERM forum online at: http://windows.lbl.gov/software/THERM/forum
---