I've explored THERM (7.4.3) for assessment of condensation risks with my students and came across some strange behavior with a very simple problem.
We built a corner of just 8" Concrete (medium weight) and applied boundary conditions of 10°F on the outside and 70°F, 60% RH (fc 1.46 BTHUh/sf.F), which brings the interior surface temperatures into a range of 56.4°F to 47.4°F in the corner - all good so far.
Now when calculating the dew point, I'd come to a temperature of 55.48°F - which would mean that some surface points are above, and others closer to the corner are below the DP - indicating a condensation potential.
THERM however shows the entire interior surface temperature at risk.
Is this now a rounding error?
I tried to set the RH to 55%, which would result in a DP of 53.09°F - still the same result, the entire interior surface is show with a condensation potential.
I then set the RH to 50%, (DP 50.51) - and suddenly there is no potential indicated any more - even though my corner reads 47.4°F. (I went into mesh view and checked the temperatures at the individual nodes)
Funny thing is that the entire interior surface "switches sides" between 52%RH and 53%, which does not correspond to the surface temperatures vs DP relationship along these boundaries.
At this point I have no explanation, other than there could be some issue as I only use one material, one domain, etc. - but I doubt that rounding is the issue here.
I can share the THM files if anyone wants to look into this.
Any pointers highly appreciated ...
Best,
Georg