Hi Diego.
Rse=0.00 m2K/W is not a refuse. It is the Rse value considered by the En Iso 6946 in case of structures in contact with ground. Obviously it must be "translated" with the highest possible film coefficient in Therm. Personally all my BC's film coefficients with Rse=0.00 are set to 99999 W/m2K.
Ciao
F.
--