Hi,
I am trying to use Therm 7.4.3 to find out if there will be interstitial condensations inside a terrace.
I used Therm to calculate temperature isotherms and I compared it to moisture condensation chart provided by an insulation manufacturer (page 3 of ManufacturerCalcs.pdf). The temperatures within the deck, as calculated in Therm, are high enough to not allow condensation inside the terrace. (The attached file Terrace Full Detail.THM).
The manufacturer of insulation is advising that there is a risk of condensation. Though, in their calculations they do not consider effects of thermal bridges and the terrace geometry. They consider the terrace energy and moisture flow only in 1 direction (ManufacturerCalcs.pdf).
When I build the detail in Therm, following the manufacturer approach, I received similar results to the manufacturer temperatures distribution (attached file: Terrace Only.THM).
I consulted this with my sustainability engineers and they advise me that they don't believe that Therm can be used for interstitial condensation assessment and they think that my approach is not correct.
Could you please advise, if my approach to interstitial condensation assessment, using Therm, is correct, i.e. comparing temperature distribution inside terrace to moisture condensation chart?
Thank you.
Maciej
Hi Toby
Thank you for your response. I am looking more for a crude assessment, than an exact solution, as there can be many details that need to be assessed, for every project.
I used Therm to model temperature distribution, assuming that if temperature will be 12ºC below slab, there will be condensation. For the sample terrace, considering that 12ºC is above the slab, the risk of condensation should be low. It is because on the top of the slab is a vapour barrier. Additionally, the insulation below the slab and the slab vapour resistance reduces the amount of moisture that can reach locations where the temperature is 12ºC. I also added a vapour barrier below the insulation that is fixed to underside of the slab.
My question would be, if Therm can model temperatures distribution accurately.
I downloaded the HTFlux software and I will test the detail.
Hi Yalin,
Thank you for your response. You noted that it is possible to use Therm to conservatively evaluate the detail.
Do you think that Therm isotherms are sufficiency accurately calculated and can be used to be compared against the dew point temperature?
My thinking was that if dew point is 12ºC degree below slab in the manufacturer calculations than if the 12ºC isotherm will be above the slab, then there should be no condensation, when looking at the dew graph (calculated in one direction). Additionally, that there is a vapour barrier, on the top of the slab, which performance is guaranteed by the manufacturer and moisture will not be able to get above the slab. I will take a look at the ASHRAE research project RP-1365.
Maciej