Hi.
There are huge variations in the prices of cables according not only to the diameter, but also the type (suitable for outdoor and / or mechanical fatigue). We should double check.
Beside this, I am pretty sure of the distance from the mast to the window of the house. I had measured it.
Regarding the DC switches, I think we should not worry too much about the insulation (it's low voltage). However, the currents may be very high : up to 700W in 12 volts, this makes nearly 60 A. The fuse for the batteries is rated at 70A anyway.
So basically, we should be able to use off-the-shelf as long as they are rated for the proper current.
It is easy for the PV panels : there is less than 110W / maybe 5 A, so an AC switch rated for 1kW should do the job.
Same for the wind turbines.
But they are not those which were bothering us as they are already connected to the charge controllers, which already can act as switches.
However, DC switches for the battery and the inverter should be rated for 70A (the fuse's rating) so that would be an AC switch rated at 16 kW !