Even i used to think PLF and CUF are one and the same thing but one
of the UNFCC CDM Executive Paper cleared my doubt to satisfactory
extents.
CUF is defined as the ratio between the gross energy generation of a
power plant and the maximum gross energy generation possible in the
period under operation, i.e (period under running condition)..say 334
days
So, number of actual operating hours = 334*24=8016
Lets say gross energy generation = 58,210,590 kWh
Installed capacity of the unit = 7.5 KW
Then CUF= (58210590/7.5*1000*8016) = 0.9682 or 96.82%
Whereas, according to the Central Electricity Authority in India, PLF
is defined as the ratio between the gross energy generation of a power
plant and the maximum gross energy generation possible in the total
monitoring period under consideration (in our case, say one year).
So, total number of operating hours is = 365*24= 8760
Then
PLF
> --
> +++++++++++++++++++++++++++++++++++++
>
> Upcoming Events
>
> Workshop on Exploring a Sustainable Future
> Auroville, Pondicherry | Sep 4-10
> http://tinyurl.com/3hguuev
>
> Course in Urban Permaculture
> Mumbai | Oct 1-5
> http://tinyurl.com/433pajt
>
> International Conclave on Climate Change
> Hyderabad | Oct 12-14
> http://www.iccc-esci.com/
>
> +++++++++++++++++++++++++++++++++++++
>
> You received this message because you are subscribed to Green-India
> to discuss India's Energy Future and Sustainable Living.
>
> Green-India
> http://green-india.in
>
> *Rules* (important)
> http://tinyurl.com/3dusax
>
> Disclaimer
> http://tinyurl.com/3gj737n
>
> To unsubscribe, send email to
> green-india...@googlegroups.com
>
--
Ahmad Mohd Khalid
Sem III, M.Tech (Renewable Energy Engineering and Management)
Department of Energy and Environment
TERI University,New Delhi
+9717832629
*Energy is what keeps the world moving.....
*
* *
Regards
Varun Mittal
MBA (2010-2012)
Department Of Management Studies
Indian Institute Of Technology Roorkee
Mobile No. 8126589577
vrn...@gmail.com
Stay green by lowering your carbon footprint.....
PLF as everybody knows it is the % loading of the thermal power plant which is calculated in terms of total generation as a % of max.possible generation.Capacity utilisation factor is not associated with a single thermal power plant, where in it is used for assessing the utilisation of grid consumption.This is being used in state of region wise and being calculated as total generation as a % of sum of all generating stations max. possible generation capacity.In general PLF evaluates performance of a single power plant. where us CUF evaluates performance of the state or region grid.Correct me if i am wrong.
Jayakumar.R,Sustenergy foundation
On Wed, Aug 24, 2011 at 5:29 PM, Akhilesh Magal <akhile...@gmail.com> wrote: