Google Groups no longer supports new Usenet posts or subscriptions. Historical content remains viewable.
Dismiss

Earth Bonding - No Earth Terminal on Incoming Mains Supply

2,101 views
Skip to first unread message

Graham Brooker

unread,
Jul 17, 2009, 11:39:27 AM7/17/09
to
I have just discovered that my house has no earth connection provided by the
electricity supply company. It has in effect an old sub mains pair of red
and black cotton/resin covered tails coming straight through the wall in the
cupboard under my stairs from next door in metal conduit. The main supply
head must be is located next door (the house next door is empty and I am
trying to trace the owner at present to gain access) which presumably has a
properly bonded earth connection point. The old red/black incoming supply
tails have a fairly modern grey main company fuse head on them but the
normal earth outlet (next to the neutral connection) has not been connected
and remains in its factory sealed/unopened state.

The electricity supply company has not provided me with an earth connection.
An electrician suggested I got access next door and ran a large earth wire
from their main earth connection through to mine. I will check what has
been done inside my consumer unit as I suspect the earth and neutral bus
bars may have been linked to provide protection.

What should I do as I intend to replace the old Wylex consumer units with a
modern 17th Edition RCD/MCB split box. I have no official earth point so
wonder what can of worms I may end up with. Is it OK to link Earth/Neutral
in my own consumer unit?

If the owner lets me in next door I can get their earth connection brought
through which is probably best. I understand that installing my own local
earth rod is not the best way forward.

Thanks

Graham

ARWadsworth

unread,
Jul 17, 2009, 2:57:33 PM7/17/09
to

"Graham Brooker" <graham....@NOSPAM.cwcom.net> wrote in message
news:G4GdncOxgPSsBv3X...@bt.com...

Hi Graham

A photo of your cut out and one of next doors would help (when you get
access). It is an odd set up but not unknown.

The most sensible thing would be to ask your supplier to supply you with an
earth.

I would suggest that you do not connect the neutral to the earth inside your
CU for two reasons.

1. You do not know if your supply is PME and if it is not then it could be
dangerous to try to make it a PME supply.

2. If you connect the neutral and earth bus bars together in a RCD CU the
RCD will almost certainly trip as soon as you turn the power on.


HTH

Adam


Graham Brooker

unread,
Jul 18, 2009, 5:51:43 AM7/18/09
to

"ARWadsworth" <adamwa...@blueyonder.co.uk> wrote in message
news:xQ38m.57628$OO7....@text.news.virginmedia.com...


>
>> A photo of your cut out and one of next doors would help (when you get
> access). It is an odd set up but not unknown.

Thanks for your advice Adam.

I will send you a photo when I have access to next door.

I certainly do not intend to do a DIY PME conversion. I am not sure what
has been done inside the old Wylex fuse box yet until we get back in there
on Monday. If a Neutral/Earth link has been been done by the previous owner
over 20 years ago then it is likely to be fairly safe as it is in a town and
is already likely to be PME in the street.

I am aware of how RCDs work and understand your comment about them tripping
if N/E is connected together. I will have to get the Electricity supplier
in at some stage but am reluctant to do so until we have improved the wring
as far as we can take it as they may well just disconnect everything leaving
us with no power to do remedial work. My electrician is able to install a
new consumer unit over the next few days and then I can call in the supplier
to provide the proper earth connection when we finally get into next door.
I am going to have to trace the owner or wait for them to respond to my
letter posted in their empty house.

I am wondering whether it will work if we upgrade to a proper dual RCD
protected CU now and put all the earth wiring in with a new main earth
connecting block ready for a proper earth connection later. I would
certainly not connect N/E together in a new RCD CU. Surely an ordinary RCD
(NOT the new type RCBO which must have its own earth connection) should not
trip if the earth is not actually present (assuming no other faults on the
internal house wring). It should be much safer than the present arrangement
while we are waiting for our proper earth connection.

What do you think?

Graham

ARWadsworth

unread,
Jul 18, 2009, 11:44:00 AM7/18/09
to

"Graham Brooker" <graham....@NOSPAM.cwcom.net> wrote in message
news:G4idneoxKqWpBvzX...@bt.com...

It is noted that you are not going to do a diy PME :-)

The RCD would offer some protection if you were to touch a live cable. Also
if your main bonding is up to standard and the water supply is metal then
there is good chance that there is already an effective earth (although the
water supply should not be used as the main earth it will work).

An RCD will not trip because there is no earth. It is more likely not to
trip! An RCD will still makes things safer. I like the idea of getting a CU
ready with an earth block waiting for the new earth.

Past experience suggests that the Wylex board will not have the earth and
neutral bars connected together. There may be an earth rod that you do not
know about but it is more likely that there is no earth at all.

A house I worked on last week had no main earth and no bonding. I took an
earth loop reading at the supply before I started work and found that it was
220 ohms. This earth was probably created by electrical connections to the
boiler etc and used the copper pipework in the house to get this earth. An
RCD would have worked with that sort of reading.

Cheers and good luck getting into next doors

Adam

Graham Brooker

unread,
Jul 18, 2009, 4:57:59 PM7/18/09
to

"ARWadsworth" <adamwa...@blueyonder.co.uk> wrote in message
news:45m8m.57994$OO7....@text.news.virginmedia.com...

Graham Brooker

unread,
Jul 18, 2009, 5:13:22 PM7/18/09
to

"ARWadsworth" <adamwa...@blueyonder.co.uk> wrote in message
news:45m8m.57994$OO7....@text.news.virginmedia.com...

>> An RCD will not trip because there is no earth. It is more likely not to
> trip! An RCD will still makes things safer. I like the idea of getting a
> CU ready with an earth block waiting for the new earth.
> A house I worked on last week had no main earth and no bonding. I took an
> earth loop reading at the supply before I started work and found that it
> was 220 ohms. This earth was probably created by electrical connections to
> the boiler etc and used the copper pipework in the house to get this
> earth. An RCD would have worked with that sort of reading.
>
Thanks for your reassurance. I have decided to fit the new CU now and run
some earth bonding to the water and gas pipes onto the new earth block/CU
internal block. The presence of RCDs will give partial protection until the
new earth connection is brought through from next door.

A few years ago I installed an isolating transformer on my boat and
disconnected the earth from the marina shoreline supply to stop galvanic
corrosion of the hull. This is standard marine practice as it stops you
getting a shock between baot and shore in the event of a fault. I bonded
one side of the secondary straight to the hull to create a "local isolated
onboard earth" so there was a reference point from which an RCD on my boat
could trip in the event of an on board fault. So I fully understand that in
this domestic case an RCD will not give a false trip because of a lack of
earth but may be less likely to work to spec until the earth is properly
connected later. I will use a combination of Land Registry and an internet
missing person trace to locate the owner if they fail to respond to my
letter at the hose. I am told the owner may be elderly so may not want to
cooperate but the electricity supplier could enforce access through the
courts if it comes to it but hopefully that will not be necessary.

Thanks

Graham

ARWadsworth

unread,
Jul 19, 2009, 6:39:44 AM7/19/09
to

"Graham Brooker" <graham....@NOSPAMcwcom.net> wrote in message
news:8sKdnSfd6uFrp__X...@bt.com...

>
> "ARWadsworth" <adamwa...@blueyonder.co.uk> wrote in message
> news:45m8m.57994$OO7....@text.news.virginmedia.com...
>>> An RCD will not trip because there is no earth. It is more likely not to
>> trip! An RCD will still makes things safer. I like the idea of getting a
>> CU ready with an earth block waiting for the new earth.
>> A house I worked on last week had no main earth and no bonding. I took
>> an earth loop reading at the supply before I started work and found that
>> it was 220 ohms. This earth was probably created by electrical
>> connections to the boiler etc and used the copper pipework in the house
>> to get this earth. An RCD would have worked with that sort of reading.
>>
> Thanks for your reassurance. I have decided to fit the new CU now and run
> some earth bonding to the water and gas pipes onto the new earth block/CU
> internal block. The presence of RCDs will give partial protection until
> the new earth connection is brought through from next door.

> A few years ago I installed an isolating transformer on my boat and
> disconnected the earth from the marina shoreline supply to stop galvanic
> corrosion of the hull. This is standard marine practice as it stops you
> getting a shock between baot and shore in the event of a fault. I bonded
> one side of the secondary straight to the hull to create a "local isolated
> onboard earth" so there was a reference point from which an RCD on my boat
> could trip in the event of an on board fault. So I fully understand that
> in this domestic case an RCD will not give a false trip because of a lack
> of earth but may be less likely to work to spec until the earth is
> properly connected later.

I had to check that you knew how an RCD worked:-) I need not have asked.

I will use a combination of Land Registry and an internet
> missing person trace to locate the owner if they fail to respond to my
> letter at the hose. I am told the owner may be elderly so may not want to
> cooperate but the electricity supplier could enforce access through the
> courts if it comes to it but hopefully that will not be necessary.

So the owner is possibly in a home or with a relative then?

Either way, s/he will have a younger relative who will cooperate with you
and save the hassle of forced entry (hopefully). Do you know if anyone is
collecting the mail from the empty house? The post might be redirected via
the post office to a different address. It could be worth a stamp to try it
out. BTDTGTTS with a house that was empty for 12 years. The owner was in a
home and all mail was redirected to her sons house.

Adam


Graham Brooker

unread,
Jul 23, 2009, 6:03:14 PM7/23/09
to
The latest news is that someone was seen next by my tenant who passed on my
phone number. The elderly lady next door seems to turn up every week or so
to clear all the mail leaving it unopened in a plastic bag in the porch.
She promised to phone me but has not done so yet. I took your advice and
posted a letter to the house in case of mail re-direction and also to the
mortgagees (taken from Land Registry) threatening court action for emergency
access.

My electrician suggested getting a PME service head fitted so I could be
independent from next door. However EDF refused and quoted between �1,500
and �2,500 for a whole new PME supply cable to the street. I would still
have to arrange access next door for them to disconnect my sub-mains tails.
It seems unfair that I should be charged to replace their old resin/cotton
cables that are considered unsafe just to save them the cost of what they
should be doing in the whole street to upgrade their network anyway. This
is more expensive than having a gas meter moved by NationalGrid! EDF would
never bond a cable clamp earth on the main supply through to my sub-mains
next door but could not stop me having this work done. The new supply cost
seems outrageous. My electrician told me they are not duty bound to provide
an earth which is why they can charge me for it. I am not sure if I can use
an earth rod which is really meant for overhead TT supplies in farms etc.

I am not sure what to do and I am hoping I will get proper contact with the
owner through their building society as it affects the security on their
loan. I am reluctant to install an earth rod in the garden which is not the
right solution. At least an RCD CU earthed the gas pipe would be a safer
temporary option while waiting for access. An internet based tracing
service had no records of the present owner at that or any other address.

Any comments welcome

Graham

Muddymike

unread,
Jul 25, 2009, 1:02:33 PM7/25/09
to

"Graham Brooker" <graham....@NOSPAM.cwcom.net> wrote in
message news:qdqdncDQW-S4Q_XX...@bt.com...

> The latest news is that someone was seen next by my tenant who
> passed on my phone number. The elderly lady next door seems to
> turn up every week or so to clear all the mail leaving it
> unopened in a plastic bag in the porch. She promised to phone
> me but has not done so yet. I took your advice and posted a
> letter to the house in case of mail re-direction and also to
> the mortgagees (taken from Land Registry) threatening court
> action for emergency access.

I have only now picked up on this thread, but if it helps I
managed to conatct the owners of an empty house via the council.
They would not give me his address but were happy to address and
post on a pre stamped letter on my behalf.

Mike


ARWadsworth

unread,
Jul 25, 2009, 1:55:51 PM7/25/09
to

"Graham Brooker" <graham....@NOSPAM.cwcom.net> wrote in message
news:qdqdncDQW-S4Q_XX...@bt.com...

> The latest news is that someone was seen next by my tenant who passed on
> my phone number. The elderly lady next door seems to turn up every week
> or so to clear all the mail leaving it unopened in a plastic bag in the
> porch. She promised to phone me but has not done so yet. I took your
> advice and posted a letter to the house in case of mail re-direction and
> also to the mortgagees (taken from Land Registry) threatening court action
> for emergency access.
>
> My electrician suggested getting a PME service head fitted so I could be
> independent from next door. However EDF refused and quoted between �1,500
> and �2,500 for a whole new PME supply cable to the street. I would still
> have to arrange access next door for them to disconnect my sub-mains
> tails. It seems unfair that I should be charged to replace their old
> resin/cotton cables that are considered unsafe just to save them the cost
> of what they should be doing in the whole street to upgrade their network
> anyway. This is more expensive than having a gas meter moved by
> NationalGrid! EDF would never bond a cable clamp earth on the main supply
> through to my sub-mains next door but could not stop me having this work
> done. The new supply cost seems outrageous. My electrician told me they
> are not duty bound to provide an earth which is why they can charge me for
> it. I am not sure if I can use an earth rod which is really meant for
> overhead TT supplies in farms etc.

Earth rods are no big deal. I have got to install one outside a cottage in a
small village next week. Correctly installed they are just as safe as PME
and TNS systems.

> I am not sure what to do and I am hoping I will get proper contact with
> the owner through their building society as it affects the security on
> their loan. I am reluctant to install an earth rod in the garden which is
> not the right solution. At least an RCD CU earthed the gas pipe would be
> a safer temporary option while waiting for access. An internet based
> tracing service had no records of the present owner at that or any other
> address.
>
> Any comments welcome

I think that you will have to wait for a reply from the mortgage company. It
is still early days and without seeing what is on the other side of the wall
then your only two options are TT or pay for a new supply.

Could you post a picture of your side of the supply?

http://tinypic.com/

seems to work well. Just post your link to your photo.

Adam


js.b1

unread,
Jul 26, 2009, 5:04:11 PM7/26/09
to
I would tell EDF to shove off and TT the supply.

This sounds like a Loop-In supply.
- Loop-in supply are illegal to install under ESQW
- Whether they be jn-box (cutout) or jn-box under your driveway
- However EDF are liable for maintaining the existing service

Thus EDF would be most grateful if you would remove their future
liability (when the supply cable blows) by paying for it yourself :-)
Tell them where to go. The distribution industry is trying to pass
every buck-cost onto the consumer.

Nothing wrong with TT.
There is a VERY remote possibility that the UK might go TT eventually.
It is expensive to maintain PME, it is expensive to maintain Ze
sufficiently low for 100A BS1361 fuses hence the practice of fitting
80A & replacing 100A with 80A.

Loop-In supplies can bite people, particularly if PME.
- Downstream neighbour loses Neutral
- 10mm MEB to lead CW & iron Gas takes house current
- No-one the wiser UNTIL they cut either pipe

Running a PME earth "next door" is certainly out as it introduces
fault currents into their house re fire risk AND leaves your earth
vulnerable to whatever anyone may do next door (such as attach it to a
screw into the wall :-). So TT as it stands is a perfectly acceptable
option. TT means you get a house disconnect on 100mA fault (time
delayed re Type-S) so you actually gain a slight fire benefit
downstream of that RCD (not that it means much in modern "30mA RCD
everything 17th regs").

Graham Brooker

unread,
Jul 27, 2009, 11:30:32 AM7/27/09
to
Hi Adam

I uploaded a photo showing a metal conduit and the L/N tails coming through
from next door into my house.

I got a phone call from the owner of the house next door. It appears she is
a landlady and she was fobbing off my tenant as they probably do not get on.
I did write a rather stern letter threatening legal action of we had to get
a court order for access. I Am going to look at it tomorrow and take a
photo for my electrician.

I will do everything possible to bring the earth through as it must be
feasible, She has had her side tested for a Housing Association let in the
past but it may no be very obvious that a second sub-mains was taken off it
if it was hidden under the meter board. Hopefully all will become plain
tomorrow.

I am reluctant to install a TT earth rod but I guess that would be cheaper
than a new supply. It may be best in the long run the have a new supply but
there are plenty of houses out there with this rather old style installation
and I would be happy with an earth clamp from next door with a new RCD CU.

Thanks for your interest

Graham

ARWadsworth

unread,
Jul 27, 2009, 12:22:04 PM7/27/09
to

"Graham Brooker" <graham....@NOSPAM.cwcom.net> wrote in message
news:gomdnVFHjdmCVfDX...@bt.com...

> Hi Adam
>
> I uploaded a photo showing a metal conduit and the L/N tails coming
> through from next door into my house.


Where?

You cannot attach the photo to your newsgoup post. You need to upload to
http://tinypic.com/ or similar and post the unique link that you have
created on their site.

Adam

Graham Brooker

unread,
Jul 28, 2009, 3:36:22 PM7/28/09
to
Sorry Adam I never used this service before. I uploaded photo to

http://tinypic.com/r/ixs6le/3

This should work OK.

I just heard from the owner next door and she promised to let me in today to
look at the mains service connection her side. She then changed her mind
(she said she had talked to her electrician and EDF who said it was not
necessary to let me connect my earth to her side) and refused to cooperate.

I am not sure why she is objecting but I think it best to try and be
independent from next door as I cannot trust her or any future owner from
tampering with my earth connection. They are less likely to interfere with
the live mains connection as it looks more serious.

My electrician will attempt to install an earth rod, which he and I do not
like, but if we can get a good earth loop impedance result then my new RCD
board should work safely. I can then decide later whether to go for a new
PME supply.

I do not think I have many other options at present as I cannot rely on the
current iron gas pipe earth which, apart from being not allowed, may end up
in plastic in the future. She will have to let EDF in to disconnect my side
anyway.

0 new messages