This has in fact been your most useful post in helping me to get much closer
to the problem...
see replies inline
news:jb7qdt$7j8$1...@news.albasani.net...
> Hi Stephen. Thanks for your descriptive advice.
>
> We had a problem with low pressure a while ago, shutting
> off the CH and HW but a fellow came and sorted it.
>
> Yeah the timer was at the right time and the settings are
> for the kids in the morning.(ŁŁŁ's got to keep the bills down)
>
> ---------
> 1...Yes the timer rotates on it's own.
>
> 2...The [3] position CH switch was in the off position so
> I could at least have Hot Water. Because when the
> CH kicks in it shuts down the boiler alltogether.
Aha!. this is the boiler's overheat protection circuit kicking in. Is there
an LCD display with a fault code or does a overheat light light up?
There are two thermistors (they measure temperature) on the flow and return
water pipes to the gas powered heating boiler cell.
The boiler electronics monitors these two temperatures via the thermistors
and calculates the difference between these two temperatures. This is called
Delta T.
If Delta T becomes too high, ie return water temp too low or flow water out
temp too high, the boiler shuts down, triggering the overheat protection
reset switch. This is an important safety feature, as if water was allowed
to turn to steam, the PRV (pressure release valve) would open and the boiler
would be damaged.
> 3...The timer switch does click when passing the pre-set times.
> ---------
>
> I turned everything off at the boiler and filled to the red arrow
> indicator.
>
> I then powered up and set the CH timer to on and also auto. Both times the
> boiler kicked in. I crossed my fingers, but after a few seconds there was
> a
> gurgling sound and the whole system shut down. (should have crossed my
> eyes also)
>
> I then switched the CH timer switch off again and took a screwdriver and
> held down
> the red reset button on top of the unit (silly place!)for a few seconds,
> which
> powered the unit once more.
This is the overheat protection cut out, see earlier of how it works.
Baiscally what is happening is when you call for central heating, that the
boiler turns on the gas valve, ignites the gas, starts the flue fan and
supplies power to the central heating pump.
If no central heating water is flowing at all or is flowing too slowly,
Delta T increased dramatically and becomes too high. This forces the boiler
to shut down. If water is indeed flowing then Delta T will
be low enough to allow the boiler to continue running.
Have you tried opening every single one of your radiator TRV's fully open
and then try running the boiler?
If you have all Radiator TRV's shut off completely then the heated water
cannot go anywhere.....
you need a minimum of at least 1 radiator fully open (otherwise the boiler
shuts down) This is usually the bathroom radiator or the radiator in the
same room as a room electronic thermostat. (the latter does not apply to you
obviously)
> So still got HW but no heating. Better than nothing I suppose
I then looked up the manual for your Worcester 350 RSF. Its actually quite
revealing........
The link is
http://www.worcester-bosch.co.uk/installer/literature/discontinued-boiler-literature/discontinued-gas-boiler-literature/350-rsf-discontinued-july-1998-literature
According to the manual, there is no diverter valve. You have actually got
two pumps, one for hot water and one for central heating.both within the
boiler.
Please don't be offended by my next sentence. It is only mentioned as I have
no knowledge of your level of technical competence.
If you are a technically competent person then fine, read on to the rest of
my post, but if you have any doubt about your own technical competence, you
could cause more problems for yourself and hence cost you more to fix the
boiler. So if you feel out of your technical depth, you really should call a
boiler engineer in.
My bet is that the central heating pump has failed or seized ( the pump on
the left when you take the cover off the boiler the pump on the right is for
hot water).
Reading through the manual suggests that if you remove the big screw in the
middle of the pump, and then start the central heating, the now exposed
shaft should rotate when you set the central heating to ON.
If it does not rotate, use a big screw driver to turn the shaft (its
possible the pump has siezed) It should then turn on its own accord. Siezed
pumps is actually common after a summer where central heating pumps don't
run at all.
On my Combi boiler, there is a programme that runs the internal pump for 5
mins a day every day, simply to stop the pump from siezing up.
As I run the hot water every day via the same pump this is a moot point, and
really is only of any value when I am on holiday (My combi has a diverter
valve which means it only needs one pump, not two.)
If the pump shaft does not turn, check for power to the pump. There is a
plastic cover on top of the pump You can take the cover off this and
measure with a volt meter. Warning, this will be at 240 volts AC so proceed
with care. There should be 240 volt power to the pump when the central
heating is being called for.
Obviously you need to measure after turning Central Heating to ON and before
the boiler shuts down due to the overheat protection kicking in.
If there is power to the pump and the pump shaft is not rotating, then pump
has failed. You will need to drain down the entire system and swap out the
pump along with new rubber "o" rings.. The part codes are in the manual.
If there is no power to the pump, then the fault lies elsewhere. Use the
fault finding chart in the manual, it will tell what to do and which part is
suspect.
Let us know how you get on.
Regards,
Stephen.