a 30amp fuse on my consumer unit has recently blow.
I`ve replaced the fuse but have noticed that it is quite hot to touch,
although still working. I assume this is not normal ?
BTW, the fuse is for an electric shower.
Any advice welcomed.
Thanks,
Johnnypanic
Is the cable warm when the shower is running (Don't try and touch it while
in the shower! lol)
--
Regards
M Millar
ICQ: 59367262
"Johnnypanic" <johnh...@anythingirish.ie> wrote in message
news:9jv738$1vd$1...@news8.svr.pol.co.uk...
Regards
Ian
M Millar <michael...@bigfoot.com> wrote in message
news:CPG87.112134$cc1.6...@nnrp3.clara.net...
Our house was only built 3 years ago and the showers were installed by the
electricians wiring the house at this time.
So it should be okay. (I hope!)
One thing I do find strange - I have another shower (exact same type) in our
ensuite. This also has a 30amp fuse, but is on the RCB protected circuits.
Is this significant ?
Thanks,
Johnnypanic
An 8.4kW shower will take about 36 amps at 230 volts so a 30 amp wired
fuse *will* get hot and, after several weeks or months will blow.
--
Chris Green (cgr...@x-1.net)
Sorry for the spelling mistake, I meant RCD.
Would it be sufficent enough to just replace both fuses (main bathroom &
ensuite) with 40amp fuses ?
Thanks,
Johnnypanic
As the house is only 3 years old I presume that the shower is protected by a
MCB if this is getting warm then there is either one of two things wrong
1) The showers current consumption exceeded the rated value of the MCB
or
2) There is heat conducted into and from a loose connection where the MCB is
affixed to the internal buss rail.
Check to see if the connections are tight, (isolate first of course :-) )
If is a semi enclosed rewireable fuse (BS3036) working at is rated current
then it will get warm after a period of time, I would suggest replacing with
a sufficiently rated MCB and for added protection a RCD as in your ensuite.
Johnnypanic <johnh...@anythingirish.ie> wrote in message
news:9k4bdl$1mj$1...@news5.svr.pol.co.uk...
--
Chris Green (cgr...@x-1.net)
[DG]uk
<ch...@areti.co.uk> wrote in message
news:S7u97.2853$LN3.6...@monolith.news.easynet.net...
"Dave" <dave...@ntlworld.com> wrote in message
news:XnG97.15229$ip4.4...@news2-win.server.ntlworld.com...
Would the trip switch not activate?
BTW, the showers is 9.5KW.
I`ll check the connections in the attic at the weekend (or should I be
giving this a higher priority ?)
Thanks,
Johnnypanic
9500W / 230V = 41A
Hardly suprising it blows a 30A fuse. Its probably only survived for so
long because cartridge fuses 'go' when the low melting point wire inside
them melts thus breaking the connection. Showers only tend to run for a few
minutes, not long enough for the fuse wire to melt through, but it will
weaken over time and eventually blow. Suggest
a) see if the cables get hot when the shower is running, if yes then your
shower is over rated for the cable - take baths!
b) call an electrician to properly check the rating of the cable & the
installation
If the installation can take the load of the shower, get the electrician to
upgrade the fuse.
If it can't, either get the installation upgraded to an appropriate cable
and fuse, or replace your shower with a lower rated one (30A fuse should
supply a 6.5Kw shower okay) - cheaper possibly but a 6.5Kw shower might not
be enough in winter.
Personally I would much rather have a circuit breaker (and RCD) on anything
electrical in the bathroom.