In the previous topic; Residential Load Calculations Spreadsheet –
Part one, I explain the steps # 1 &2 and today, I will continue
explaining the remaining steps as follows:
Step 3- info: Equipment set-up worksheet
Original loads were used from the average appliance loads for the GE
appliance guide. Now you can customize HVAC and appliance loads by
means of an equipment set-up sheet with fixed and new entry cells as
follows:
1. Blue cells are fixed loads and the first value is default.
2. Yellow cells to insert your own personal entries, enter numerals
only and don’t type VA.
Step 3: Article 220.53
Appliance load – dwelling unit(s). it shall be permissible to apply a
demand factor of 75 percent of 75 percent to the nameplate rating of
four or more appliances fastened in place, other than electric ranges,
clothes dryers, space heating or air-conditioning equipment, that are
served by the same feeder in a one family, two family, or multifamily
dwelling.
1-Insert the load of fixed appliances from the drop down boxes (see
equipment set-up worksheet for adding your own loads)
Appliances:
• Water heater
• Refrigerator
• Freezer
• Dishwasher
• Disposal
• R/ hood
• Microwave
• MICROWAVE: use the capital letter name in case of microwave load is
120 V connected by checking the box
• Mini Refrigerator
• Wine cir: if the load is 120 V connected, check the box) (Use this
space for other appliances or equipment not listed in steps 4 and 5.
Enter a short name and loads on equipment setup sheet
• Instant hot: : if the load is 120 V connected, check the box) (Use
this space for other appliances or equipment not listed in steps 4 and
5. Enter a short name and loads on equipment setup sheet
• Ironing center: enter the number of circuits to built-in ironing
centers
• Jacuzzi tub: check the box to the left if motor is neutral connected
ad it shall be included in the demand calculation
• Sprinkler pump: check the box to the left if motor is neutral
connected ad it shall be included in the demand calculation
• Well pump: check the box to the left if motor is neutral connected
ad it shall be included in the demand calculation
• Fountain pump: or enter the name for other motor load) (demand
factor for 4 or more appliances will not be applied
• Elevator: or enter the name for other motor load) (demand factor for
4 or more appliances will not be applied
• Pool equipment panel: enter pool equipment or equipment connected to
this panel below and the total will be inserted in the cell to the
right (demand factor for 4 or more appliances will not be applied)
(100% demand)
• Gates: if the load is 120 V connected, check the box to the left,
and Check the box to the right and this load will be computed with the
appliance demand factor (Enter the volt amps for this load, and enter
the name of the load for other appliances for equipment not listed in
steps 4 and 5.) (No demand)
• Other loads: if the load is 120 V connected, check the box to the
left, and Check the box to the right and this load will be computed
with the appliance demand factor (Enter the volt amps for this load,
and enter the name of the load for other appliances for equipment not
listed in steps 4 and 5.) (No demand)
2- Insert the total number of the following fixed appliances in the
yellow cells (except Gates and other loads
Outputs:
a-Total appliance load: this is the total sum of appliances before
applying demand factor)
b-Total appliance demand load: 4 or more demand @ 75% plus 100% demand
loads (in article 220.53)
Step 3 - pool: Pool equipment panel (3-Wire or 2- wire, single phase
service)
Locally the AHJ were requesting the pool equipment loads be shown with
pool heat pumps calculated @ 125% as continuous loads (3 hour or
more).
1-Select by drop down boxes the size of motors based on horse power
2-Check the box to the right of the motor if neutral connected to
change from 240V to 120V so that the phase and neutral loads will be
included in the calculation
Note (1): Only the largest motor @125 % regardless to the column and
other motors @100%
Note (2): Automatically a pool pump selected from the continuous drop
down box the VA is multiplied by 125%. If you then select a 3.5 or 5
ton heat pump, the heat pump becomes the largest motor and the
continuous motor value changes to 100%.
Note (3): SPA and pool heater in this panel shall be calculated @125%
as a continuous load.
3- Select by drop down box the pool lighting load based on standard
transformer sizes or group of multiple transformers
4- Select SPA blower by motor horse power and check box for voltage
Note (4): Do not enter loads in step #3 that you are entering here in
this panel, this loads will be totaled and shown in the field “ Pool
Equipment Panel”
5- Two spaces are provided for other loads like a sprinkler pump,
grill, landscape lighting, etc., enter a short description, the volt-
amperes of each and select the voltage
6- Check the box to change the pool feeder from Cooper to aluminum.
to read more, please follow the below link: