Hi,
I have a question about sprinkler temperature in an FDS model. Thanks for taking the time to read my question below:
I am doing a sensitivity check for my FDS models with different mesh sizes of 0.1m, 0.2m and 0.4m.
I am using a quick response sprinkler, the activation time of the sprinkler is 68C, the code is below:
&PROP ID='Commercial Spray',
QUANTITY='SPRINKLER LINK TEMPERATURE',
ACTIVATION_TEMPERATURE=68.0,
RTI=50.0,
C_FACTOR=0.65,
PART_ID='Water',
FLOW_RATE=56.1,
PARTICLE_VELOCITY=5.0,
SPRAY_ANGLE=60.0,75.0/
I also have a freeze time control to stop the heat release rate (HRR) from increasing once the sprinkler is activated at around 68C.
In the 0.2m and 0.4m mesh size model, all the sprinklers' temp reduce to the ambient temperature of around 20C immediately after sprinklers reach close to 68C.
However, in my 0.1m mesh size model, after 68C, the sprinkler temperature still keeps raising to around 85C then remains unchanged, and it does not decrease to the ambient temperature. And I saw the freeze time control is activated when the sprinkler temp reaches around 67C as the HRR stops increasing from this point. So except for the sprinkler temp, all the other things look reasonable.
Does anyone know the reason the sprinkler temp keeps raising to 80-90C and is not reduced to the ambient temperature?
Many thanks!