Hi,
I've had a look at Pyrosim, and it looks like I have to manually create the control function (correct me if I'm wrong!) to combine both smoke detection and deadband input. I've had a look at the FDS manual, and I'm having trouble understanding how to formulate the code.
For example (using this extract from the manual), I have this deadband control...
&SURF ID='FAN', TMP_FRONT=40., VOLUME_FLOW=-1. /
&VENT XB=-0.3,0.3,-0.3,0.3,0.0,0.0, SURF_ID='FAN', CTRL_ID='corridor' /
&DEVC ID='TC', XYZ=2.4,5.7,3.6, QUANTITY='TEMPERATURE' /
&CTRL ID='thermostat', FUNCTION_TYPE='DEADBAND', INPUT_ID='TC',
ON_BOUND='LOWER', SETPOINT=23.,27., LATCH=F/
and I want to also consider the smoke detector input (extracted from Pyrosim)...
&CTRL ID='corridor', FUNCTION_TYPE='ALL', LATCH=.TRUE., INPUT_ID='or'/
&CTRL ID='or', FUNCTION_TYPE='ANY', LATCH=.FALSE., INPUT_ID='SD','SD01'/
How would you go about formulating the code?
Many thanks in advance.