Your VENT for the NITROGEN is commented out in this input file. Is this the exact file you used? If so, then the issue is with the VENT commented out you have no NITROGEN being added.
If you did run a version of this without the VENT and its CTRL commented out a few comments:
-You have a lot of OPEN VENTs in the domain. Gasseous suppression requires that a sufficient concentration of the agent be maintained to keep the fire suppressed. OPEN VENTs are going to allow NITROGEN to leave the domain and AIR with oxygen to enter the domain.
-The EXTINCTON 2 model in FDS says combustion is allowed as long as there is fuel and oxygen present above the AUTO_IGNITION_TEMPERATURE with enough fuel and oxygen to reach the CRITICAL_FLAME_TEMPERATURE. You have an AIT of 215 C which means all it takes is some gas cell somewhere to be above that temperature while there is fuel and oxygen present to reach the CFT to reignite the fire. You also have an AIT exclusion zone where it all it takes is having fuel and oxygen present to reach the CFT for the fire to burn. If the fire reignites somewhere that heat addition can result in more cells reaching the AIT and being able to burn
-Your WOOD surface has an IGNITION_TEMPERATURE and an HRRPUA. One a wall cell reaches the IGNITION_TEMPERATURE it will emit HRRPUA of fuel for the remainder of the simulation. With these inputs, there is no coupling between heat feedback and the size of the fire once the IGNITION_TEMPREATURE is reached.
-You may want to add slice files for NITROGEN, OXYGEN, and REAC_FUEL plus EXTINCTION. This will let you see where exticntion is occuring and the conditions that are present in those locations. It may help you better understand what is happening in your simulation.
Yes, I have set up AIT and also set up AIT_EXCLUSION_ZONE. Is this kind of resurgence bound to happen? Or am I missing some settings? Could you please help me take a look?