18.4.2 Activating and Deactivating Vents
When a device or control function is applied to a VENT, the purpose is to either activate or deactivate any time ramp associated with the VENT via its DEVC_ID.
The 'fire' BC is always being applied to the OBST. What the DEVC controls is the RAMP for the fire size and the implied RAMP for TMP_FRONT=0 (the default TAU_T=1). With your inputs, there is no 1D heat conduction for 'fire' which is why your DEVC is not showing a temperature change.
Remove the SURF_ID='wood' from the OBST and add it to the five VENTs. Then take the HRRPUA and RAMP_Q inputs from fire and copy them to the wood SURF. Now the five faces with wood will heat up and when the DEVC activates the RAMP_Q will start.