LOSS is the loss coefficient, K not the pressure drop in the duct. The pressure drop (head) is given by 1/2 rho K V^2. In your first case there is no driving force for there to be any flow. What you have is a piece of duct at an angle. If you were to pick up a horizontal length of duct and rotate it vertically, you will not suddenly see flow.
In your second case you have defined a fan curve; however, your fan curve says that at zero pressure across the fan, that there is zero flow. At t=0, there is no net pressure at the fan. The difference in static pressure between the endpoints of the duct is exactly balanced by the weight of the air in the duct. Your fan curve is also non-physical. Look at the example in the user's guide. The volume flow should decrease with increasing pressure. Your fan curve says the fan moves more air the harder it has to work against pressure.
In the third case if you had a valid fan curve then the flow would be where dP_fan = 1/2 K rho v^2. Since your duct is 0.1 m^2 this is dP~0.5 * 10 * 1.19 * vdot /0.1