See Eq 10.3 in the Tech Reference. The fan pressure appears in the delta p_j term in the equation. It's value can range between 0 and the stall pressure depending on the current volume flow rate in the duct. If, for example, you reach a point where the flow in the duct is at the maximum flow, then the fan will not add any additional pressure and the flow rate will solely depending upon the node pressures. If on the other hand then flow rate reaches zero, then the fan will add the maximum pressure to the node pressure difference. If the pressure difference winds up negative there will be reverse flow.
Figure 12.5 plots the quadratic curve, the custom curve as defined in the example, and a constant flow curve. These are all made up inputs and did not come from any specific manufacturer. Manufacturers do not typically measure fan performance curves outside the range of 0 flow (stall pressure) to max rated flow. The fan blades, fan housing, etc. do impose flow losses. These are already accounted for in the fan curve. If you need to develop a fan curve beyond these points extrapolating assuming quadratic behavior at the ends of the curves should give you reasonable behavior. Unless you have a highly sealed room, typical leakage areas should limit the ability to drastically exceed the limits of the fan curve.
Try using DUCT_ID.