Soot yield

61 views
Skip to first unread message

Hosein Sadeghi

unread,
Sep 27, 2022, 8:15:18 AMSep 27
to FDS and Smokeview Discussions
Hi,
According to the user guide, soot yield is calculated as
y_s= nu_s*W_s/W_f

If a reaction is defined as
a(C_x1 H_y2 )+ b(C_x2 Hy_2)+ Air -> products + nu_s*Soot

is it correct to calculate soot yield as

y_s=nu_s* W_s/ (a*W_f1 + b*W_f2)

where W_f1 and W_f2 are the molar weights of C_x1 H_y2 and C_x2 Hy_2, respectively.


BR,
Hosein

Kevin McGrattan

unread,
Sep 27, 2022, 8:48:22 AMSep 27
to fds...@googlegroups.com
SOOT_YIELD is appropriate for the single reaction model. If you want to consider two fuels, you need to define all reactants and products explicitly.

Hosein Sadeghi

unread,
Sep 27, 2022, 9:33:35 AMSep 27
to FDS and Smokeview Discussions
Thank you. I am defining the fuels as a lumped mixture, similar to section 15.2.2.

Randy McDermott

unread,
Sep 27, 2022, 9:38:07 AMSep 27
to fds...@googlegroups.com
Your definition is correct.

--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/b81cd639-6114-4997-947a-c3e9c295114an%40googlegroups.com.

Hosein Sadeghi

unread,
Sep 27, 2022, 9:40:17 AMSep 27
to FDS and Smokeview Discussions
Thank you.