Mech. smoke ventilation using HVAC, controled by an timer

62 views
Skip to first unread message

tobi br.

unread,
Nov 17, 2021, 2:29:44 AM11/17/21
to FDS and Smokeview Discussions
Hey

i tried to code a mechanical smoke ventilation using HVAV.

A very similar code worked out good before. Now theres a problem with the timer.

Code for the HVAC

&DEVC ID='Timer01', XYZ=0.0,0.0,0.0, QUANTITY='TIME', SETPOINT=0, / 
&CTRL ID ='MRAON', FUNCTION_TYPE='ANY', INPUT_ID='TIMER01'/
&DEVC ID ='Flow_MRA', QUANTITY='VOLUME FLOW', XB= 16.3,18.3,18.9,20.9,5.8,5.8, /
 
&VENT ID='MRA_IN', SURF_ID='HVAC', XB= 16.3,18.3,18.9,20.9,5.3,5.3, CTRL_ID='MRAON'/
&VENT ID='MRA_OUT', SURF_ID='HVAC', XB= 16.3,18.3,18.9,20.9,5.8,5.8, CTRL_ID='MRAON'/

&HVAC ID='IN', TYPE_ID='NODE', DUCT_ID='Duct01', VENT_ID='MRA_IN', CTRL_ID='MRAON'/
&HVAC ID='OUT', TYPE_ID='NODE', DUCT_ID='Duct01', VENT_ID='MRA_OUT', CTRL_ID='MRAON'/

&HVAC ID='Duct01', TYPE_ID='DUCT', AREA=2.0, PERIMETER=8.0, VOLUME_FLOW=3.0,
NODE_ID='IN','OUT', ROUGHNESS=1.0E-3, LENGTH=1.4, CTRL_ID='MRAON'/ 


This Error  occurd:

ERROR: VENT 7 must be a plane (MPI Process: 0, CHID: FDSSMV_PRUEFUNG2)

 DEVICE Activation Times

   1  timer                                                       No Activation

ERROR: FDS was improperly set-up - FDS stopped (CHID: FDSSMV_PRUEFUNG2)


Anyone knows how to fix this error?

Cheers!

dr_jfloyd

unread,
Nov 17, 2021, 5:03:01 AM11/17/21
to FDS and Smokeview Discussions
The error is saying that the input line for 7th VENT in your input file is not a plane.  Check the inputs for the 7th VENT.

Do not use CTRL or DEVC for VENTs tied to HVAC.  From 12.2.3 "'Note that a VENT being used for an HVAC system should not have a CTRL_ID or DEVC_ID. If you need
to turn on or off a VENT connected to an HVAC system, use a damper in the duct connected to VENT."