Just to add in some discussion Craig and I had off the board and my understanding of it. This approach should work, but depending on the conditions in the submitter's actual model, he may not see suppression at 16.9%. At the time the model hits 16.9% and suppression is expected, Cp (1.2) may not be exactly correct, but Tm, the control volume bulk temperature, is not likely 293K. Its probably higher, which means the oxygen level at suppression is going to be lower. So should X_LL_O2 be added back in as an input or not? Craig makes the very fair point the if the data for the suppression O2 is known, knowledge from that experiment could/should be used to do this calculation a little more properly. But the result is that it may not suppress at the same O2 level. Now, making this adjustment based on temperature is probably a more correct answer. But if the user, for whatever reason, can guarantee suppression at a particular O2 level, should it be an input or not? Or maybe just a little bit of text in the appendix should be added to note that, when using this approach, one is calculating the critical flame temperature for suppression in ambient temperature conditions, and that suppression will likely occur at some lower oxygen concentration.
Stephen.