Is there any validation work with FDS that compares velocities, mass
flow or volume flow through natural vents? My experience with FDS,
using a relatively coarse mesh ( about 10 grid cells across the
natural vent) is an over prediction of the volume- and mass flow
compared to a simple hand calculation( Bernoulli).
I use the pressure across the vent (some horizontal distance from the
vent), actual vent area (number of cells) and temperature from FDS.
The flow coefficient for the hand calculation is obtained from the
literature (0,6-0,7). The volume- or mass flow from FDS is obtained
with the volume- or mass flow function in FDS. Has anyone experienced
similar trends? I am using a HOLE by the way.