Soot visibility

769 views
Skip to first unread message

clem...@tpi.setec.fr

unread,
May 28, 2010, 9:00:15 AM5/28/10
to FDS and Smokeview Discussions
I have e few questions concerning the soot visibility.
I am simulating fire in tunnel and we need to approximate the
visibility there is in the tunnel, to know if the users will be able
to see the emergency exit.

I am using the slice with the quantity "soot visibility"
The dimension of this quantity is meter.

The theory I read about the visibility in fire is :

The visibility is relative to what you are watching. You can see a
light at 30 meters but don't see a road sign at 5 meters. That depends
on the opacity of the smoke.

In the tunnel's norm, they use the opacity of the smoke which can be
directly linked with the visibility with a coefficient depending on
the road sign.

In FDS what are the standards you took to say that the visibility is
20meters for example. How are you claculating that ? Do you refer to
the opacity too ? And if yes, which coefficient do you use to
calculated the visibility ?

Thanks for your help !

dr_jfloyd

unread,
May 28, 2010, 9:35:16 AM5/28/10
to FDS and Smokeview Discussions
User's Guide 14.3.2

On May 28, 9:00 am, "clemen...@tpi.setec.fr" <clemen...@tpi.setec.fr>
wrote:

S.Desanghere

unread,
May 29, 2010, 12:36:51 PM5/29/10
to FDS and Smokeview Discussions
The visibility distance is calculated by FDS by the formula:

S = C / (Km * rho * Ysoot) [in meter]

with C = 3 and Km = 8700 m²/kg by default. When there is no soot
(Ysoot=0), S should be infinity. In FDS, the maximum value for S is 30
m (arbitrary choice).

Ysoot is the local value of the mass fraction of soot (deduced from
the mixture fraction calculation: so the way you define the combustion
reaction matters ! (soot yield)).

S is the visibility distance within a homogeneous medium whose soot
concentration is Ysoot. As a consequence, this estimation is wrong for
instance if you are in a small zone without smoke which is surrounded
by smoke. In this case, you should see a kind of "smoke wall". You
have to solve the radiative transport equation to treat such a case.

Finally, I suggest you to read the following reference :

http://fire.nist.gov/bfrlpubs/fire02/PDF/f02072.pdf

Cheers
Sylvain