----- Original Message -----From: dr_jfloyd
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To view this discussion on the web visit https://groups.google.com/d/msg/fds-smv/-/y90GioHVK6cJ.
----- Original Message -----From: dr_jfloyd
Sent: Wednesday, August 10, 2011 1:43 PMSubject: Re: [fds-smv] Re: Visibility criterion
A thought has occurred. Are you comparing the same numbers? In the 8.7 m^2/g, the g is grams of soot. If the 1 m^2/g number comes from a large scale fire (where measuring the soot mass would not be easy) is that g grams of fuel (as in soot obscuration produced per mass of fuel)? If that is the case and one assumes something like a 10 % soot yield then 1 m^2/g of fuel would become 10 m^2/g of soot.
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To view this discussion on the web visit https://groups.google.com/d/msg/fds-smv/-/sJ_OoWIejTMJ.
----- Original Message -----From: dr_jfloydSent: Wednesday, August 10, 2011 10:39 PMSubject: Re: [fds-smv] Re: Visibility criterion
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To view this discussion on the web visit https://groups.google.com/d/msg/fds-smv/-/SOlpIaifnawJ.
As I stated you are not comparing the same measurements. FDS uses 8700 m2/g of SOOT. The Heskestad number is per g of FUEL. Yes the numbers are different, but they are measuring TWO different quantities. In your example convert the 1 m2/g of fuel to g of soot by using the 0.075 soot yield which by the way would make it 13 m/g of soot an even larger value than we use in FDS
In the coarse of these discussions, one may conclude that there is an
evidence that the popular software uses small-scale measurements to compute
visibility. Namely, in some tests of Mulholland and Croakin's work the
chamber was 1 m3. In Gottuk's tests measurements were made at 4.6 m from the
fire, and the discrepancy with the computed prediction was large.
Mulholland reports on the considerable agglomeration of soot clusters. Can
this agglomeration be the reason for the deviation of the large-scale test
data from the computed results? The agglomeration of smoke particles may
result in decrease of the extinction coefficient. Otherwise, it is difficult
to understand: why smoke changes while floating.
It would be of great assistance to get the opinions on this issue.
Victor Shestopal
Australia
----- Original Message -----
From: "Bogdan Dlugogorski" <bogdan.dl...@newcastle.edu.au>
To: <ia...@newcastle.edu.au>
Sent: Wednesday, August 10, 2011 6:11 AM
Subject: IAFSS> Re: Visibility criterion
>>>> Dan Gottuk <DGO...@haifire.com> 10/08/2011 5:32 am >>>
> We concur with the smoke production issue mentioned below. We have
> conducted tests and compared published small-scale smoke yields to larger
> scale fires. The measured soot yields for 100 kW fires range from 2 to 5
> times smaller than the reported small-scale values. This finding was
> reported in our 2008 IAFSS paper:
>
> Gottuk, D., Mealy, C., and Floyd, J., "Smoke Transport and FDS
> Validation," Fire Safety Science - Proceedings of the 9th International
> Symposium, International Association of Fire Safety Science, Karlsruhe,
> Germany, September 21-26, 2008, pp. 129-140.
>
> We also found that for some situations there can also be up to 40% soot
> loss due to deposition on a ceiling above the plume. This type of soot
> loss has not generally been taken into account in models.
>
> Regards,
> Dan Gottuk
>
> Daniel T. Gottuk, Ph.D., P.E. | Senior Engineer | Hughes Associates, Inc.
> 3610 Commerce Drive | Suite 817 | Baltimore, Maryland 21227
> Tel: 410.737.8677 x 217 | Cell: 443-310-5558 | www.haifire.com
>
>
>
>
> -----Original Message-----
> From: iafss-...@newcastle.edu.au
> [mailto:iafss-...@newcastle.edu.au] On Behalf Of Bogdan Dlugogorski
> Sent: Tuesday, August 09, 2011 2:54 PM
> To: ia...@newcastle.edu.au
> Subject: IAFSS> Re: Visibility criterion
>
>>>> Atle William Heskestad <AtleWillia...@sintef.no> 9/08/2011
> 9:53 pm >>>
> Dear all
>
> There has been some internal communication on the issue between Victor
> and me, and which can be summarized to that small scale test data for
> smoke might be as much as 10 times too high compared to experimental
> data from large scale fire testing.
>
> In my thesis there was shown that small scale tests might produce far
> more smoke than what is measured in large scale test. This was revealed
> by comparing experimental smoke data normalized to heat release (i.e. to
> oxygen consumption).
>
> Thus references have to be used with care, especially when several
> references are combined in simulations. The crucial issue is to use
> consistent input data, which means that input data have to originate
> from the same fire conditions.
>
> For those further interested in the issue, there was made a paper by
> Anne Steen-Hansen and me on the Human behavior fire symposium in 2001.
> The paper shows the visibility conditions compared to the toxic
> conditions by use of experimental data made by SINTEF NBL in connection
> with the investigation on the Scandinavian ferry disaster. The paper is
> also available through the PhD-thesis to Anne, which can be downloaded
> from the home pages to NTNU.
>
> The mentioned reference deals only with experimental data. I am not
> aware of any publications on simulations of smoke atmospheres including
> the visibility conditions, and where the simulations are verified with
> large scale experimental data. Some CFD computational tools might be
> capable on such computations, but I have not seen such simulations
> compared with experimental data originating from large scale fires.
> Please let me know if such references are available.
>
> Best regards, AtleW Heskestad
>
>
>
> From: Victor Shestopal [mailto:fire...@optusnet.com.au]
> Sent: 5. august 2011 01:32
> To: iafss...@newcastle.edu.au; ia...@newcastle.edu.au;
> ia...@cc.newcastle.edu.au
> Cc: Atle William Heskestad
> Subject: Visibility criterion
>
> Dear Dr Heskestad,
>
> Your message has very important qualitative information.
> To use this information in our practical engineering work, some
> quantitative hints would be also important. Below are several lines of
> one of my report summarizing results obtained using FDS5 (fuel is
> polyurethane) :
>
> The maximum temperature at the height of 2.1 m in 25 minutes is
> below 43*C everywhere...
> The maximum concentration of carbon monoxide at the height of 2.1 m
> above the floor in 25 minutes after ignition is below 350 ppm
> everywhere...
> The visibility of 10 m at the height of 2.1 m will be maintained for
> not more than 2.5 minutes. However, at the height of 1.4 m above the
> floor the visibility of 5 m will be maintained for 8 minutes.
>
> I do not believe that such results might be realistic. The requirement
> to maintain visibility causes extra spending to our clients. For the
> entire industry this is millions of dollars.
>
> Victor Shestopal
> Australia
>
>
>
> Iafss mailing list
> Ia...@newcastle.edu.au
> http://mailman.newcastle.edu.au/mailman/listinfo/iafss
> **********************************************************************
> THIS DISCUSSION FORUM IS OPERATED BY THE INTERNATIONAL
> ASSOCIATION FOR FIRE SAFETY SCIENCE. THE ASSOCIATION HOLDS
> TRIENNIAL SYMPOSIA, PUBLISHES THE FIRE SAFETY JOURNAL,
> PROVIDES ITS PUBLICATIONS AT A DISCOUNT TO ITS MEMBERS AND
> ENGAGES IN OTHER LEARNED ACTIVITIES OF BENEFIT TO THE FIRE
> SCIENCE AND ENGINEERING COMMUNITY. THE ANNUAL MEMBERSHIP
> FEE IS ₤21 (or equivalent in US$); THE FEE IS ₤11 FOR
> STUDENTS. CONTACT
> iafssm...@dial.pipex.com FOR MEMBERSHIP SUBSCRIPTION.
> **********************************************************************
>
> **********************************************************************
> Views, opinions and information presented here are not necessarily
> those of the International Association for Fire Safety Science and/or
> the Society of Fire Protection Engineers. To subscribe visit
> http://mailman.newcastle.edu.au/mailman/listinfo/iafss (for IAFSS
> Discussion Forum)
> or http://mailman.newcastle.edu.au/mailman/listinfo/sfpe (for SFPE
> Discussion Forum). At present, both Fora co-share their postings.
> **********************************************************************
>
> Iafss mailing list
> Ia...@newcastle.edu.au
> http://mailman.newcastle.edu.au/mailman/listinfo/iafss
> **********************************************************************
> THIS DISCUSSION FORUM IS OPERATED BY THE INTERNATIONAL
> ASSOCIATION FOR FIRE SAFETY SCIENCE. THE ASSOCIATION HOLDS
> TRIENNIAL SYMPOSIA, PUBLISHES THE FIRE SAFETY JOURNAL,
> PROVIDES ITS PUBLICATIONS AT A DISCOUNT TO ITS MEMBERS AND
> ENGAGES IN OTHER LEARNED ACTIVITIES OF BENEFIT TO THE FIRE
> SCIENCE AND ENGINEERING COMMUNITY. THE ANNUAL MEMBERSHIP
> FEE IS ₤21 (or equivalent in US$); THE FEE IS ₤11 FOR
> STUDENTS. CONTACT
> iafssm...@dial.pipex.com FOR MEMBERSHIP SUBSCRIPTION.
> **********************************************************************
>
> **********************************************************************
> Views, opinions and information presented here are not necessarily
> those of the International Association for Fire Safety Science and/or
> the Society of Fire Protection Engineers. To subscribe visit
> http://mailman.newcastle.edu.au/mailman/listinfo/iafss (for IAFSS
> Discussion Forum)
> or http://mailman.newcastle.edu.au/mailman/listinfo/sfpe (for SFPE
> Discussion Forum). At present, both Fora co-share their postings.
> **********************************************************************
I am not sure if agglomeration would be significant over the time range we are dealing with. Have you computed an agglomeration kernal to see what rate would be expected?
You write "Once we had a fuel with a similar yield to the fds simulations,
we saw comparable results of visibility in the plume". Where these results
can be seen? Are any publications or reports? Please provide an evidence.
So far, in your and Daniel Gottuk's paper there is something different (page
137, bottom): "it is important that the model input was a fire with a soot
yield of 2.2 percent and the experimental tests used a fire with a soot
yield of 4.8 percent... it became apparent that soot loss was a substantial
phenomenon that had to be considered".
Further clarification would be very helpful.
Regards,
Victor Shestopal
Australia
.
----- Original Message -----
From: "dr_jfloyd" <drjf...@gmail.com>
To: <fds...@googlegroups.com>
Sent: Friday, August 12, 2011 10:53 PM
Subject: [fds-smv] Re: Visibility criterion
> --
> You received this message because you are subscribed to the Google Groups
> "FDS and Smokeview Discussions" group.
> To view this discussion on the web visit
> https://groups.google.com/d/msg/fds-smv/-/oDV09Fd_cmQJ.
Hi all,