I have a validation question with regards to the reports from Rein and
validating a FDS model with empirical data.
As Rein describes (above), in the atria FDS seem to overpredict the
temperatures closer to the flame and slightly underpredict the
temperatures higher up. I get similar results when conducting a grid
sensitivity analysis and comparing to Heskestad plume temperatures
(thanks kevin). I used 0.0625, 0.125, and 0,25 m grids to for a
uniform mesh for a 2MW fire with 1m x 1m base and shaft extending 45m
up. The drew the conclusion that 0.0625 and 0.125 produce similar
results for this setup, hence I want to use the 0.125 grid for
modeling for time reasons.
I have a few questions about this sensitivity analysis:
1) I'm interested in good results "far" away from the fire where the
modeled results seem to converge with the empirical ones. What happens
if I model the same fire in a room only 4 metres high? Is the grid
sensitivity analysis no longer valid for this case? Would the model
give me good comparison with Mccaffrey plume model if I did it
correctly? I find things get complicated once I'm in the flame :)
2) I'm using exhaust vents with 10 m3/s capacity. Some of the vents
are located further away from the fire where the grids are coarser (up
to 0,5 metres). Since the exhaust vents is "action" territory, do I
need a finer grid here as well? If yes, do I need the finer grid from
the fire, all the way up to that vent?
3) The design fire is a 2MW fire. Because of the complexity of subject
furniture such as chairs of unknown quality etc I have used heptane
with a HRR of 2MW. Instead of a heptane fire with an area of
0,4347..m2 I used a 1m2 burner with HHR 2000kw/m2.
The "Reaction" line only used for species etc, correct? Do I give up
any accuracy of calculation with this approach with regards to
temperatures, smoke fill etc? (since there wont be a heptane pool
there anyway, but stacked chairs etc)
Warm regards,
Henrik