EXTINCTION model

321 views
Skip to first unread message

Khalid Moinuddin

unread,
Dec 7, 2023, 11:43:46 PM12/7/23
to FDS and Smokeview Discussions

Until version 6.7.9, the default EXTINCTION model for VLES was EXTINCTION 2.  However, now (6.8.0), the default EXTINCTION model for VLES is EXTINCTION 1.  

What is the rationale behind such change? 


Jonathan Hodges

unread,
Dec 8, 2023, 7:23:21 AM12/8/23
to FDS and Smokeview Discussions
Extinction 2 relies on resolving high temperatures of the flame which generally will not be resolved in VLES. For the most part this change does not impact users. While the extinction model is technically active by default, the AUTO_IGNITION_TEMPERATURE is set at 0 K unless the user specifically sets it.

dr_jfloyd

unread,
Dec 8, 2023, 9:09:49 AM12/8/23
to FDS and Smokeview Discussions
Ignition in FDS requires the cell temperautre be over the A_I_T and that gas contents of the cell pass an extinction check. EXTINCTION 1 only uses the cell temperature. EXTINCTION 2 uses the cell temperature and the cell gas concentrations. For applications where you are well ventilated there should be little effect other than EXTINCTION 1 was not sensitive to high molecular weight fuels species without user defined thermophysical properties. For underventilated fires and coarse grids we noticed  that EXTINCTION 2 was resulting in too much extinction. 

Khalid Moinuddin

unread,
Dec 8, 2023, 3:25:19 PM12/8/23
to FDS and Smokeview Discussions

Thanks, Jonathan and Jason.

 

 

 

From: fds...@googlegroups.com <fds...@googlegroups.com> On Behalf Of dr_jfloyd
Sent: Saturday, 9 December 2023 1:10 AM
To: FDS and Smokeview Discussions <fds...@googlegroups.com>
Subject: [fds-smv] Re: EXTINCTION model

 

EXTERNAL EMAIL: Please be cautious before clicking on any links or downloading attachments.

 

--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/c3717423-71bc-4619-8c11-5da67449c437n%40googlegroups.com.

Iqbal

unread,
Dec 14, 2023, 8:01:19 PM12/14/23
to FDS and Smokeview Discussions

Hello, I am following the discussions and some more details is requested for the clarification regarding their implementation.

I have intend to employ Very Large Eddy Simulation (VLES) for modeling, taking into account an Auto-Ignition Temperature (A_I_T) set to 215 degrees Celsius for Heptane, utilizing a grid size of 50 mm or less, and with adequate/small ventilation. How the use of EXTINCTION 2 or EXTINCTION 1 is going to affect the suppression?

Considering Jonathan's discussion, as VLES does not resolve the high temperature of the flame, the use of EXTICNTION 2 will not give any further benefit.

Regards

Iqbal

Jonathan Hodges

unread,
Dec 16, 2023, 7:24:43 AM12/16/23
to FDS and Smokeview Discussions
Since the AIT of Heptane is relatively low, I expect you would get similar results between EXTINCTION 1 and 2, but it would be interesting to see in your case. Where I have personally seen a larger difference is in fuels with AIT in the ~500 C range and you get interesting interactions with compartment fire dynamics with flashover temperatures.

H. M. Iqbal Mahmud

unread,
Dec 18, 2023, 6:25:21 PM12/18/23
to fds...@googlegroups.com
Thanks Jonathan. 
I am planning to use the model EXTINCTION 2 in VLES to simulate fire extinguishment with AIT.
Let's see how it goes.


--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.

Iqbal

unread,
Jan 24, 2024, 11:46:58 PM1/24/24
to FDS and Smokeview Discussions
Hi There, 
One more thing to clarify- If I use EXTINCTION 2 in SVLES mode, instead of the default EXTINCTION 1 model, how is it going to affect the suppression?
As mentioned by Jonathan Hodges in this link- "Since the AIT of Heptane is relatively low, I expect you would get similar results between EXTINCTION 1 and 2". Is this that this comment is also applicable for SVLES?
Thanks for your cooperation.

Kevin McGrattan

unread,
Jan 25, 2024, 6:54:44 AM1/25/24
to fds...@googlegroups.com
If you are using SVLES, use EXTINCTION 1. EXTINCTION 2 is intended for simulations with relatively fine resolution, like cells on the order of a few centimeters.