Your experimental data does not look right to me. In my experience, CO
measurements are sometimes erratic because the production rate of CO
is not necessarily constant, especially for bigger fires. But the CO2
increase and the O2 decrease should look much like the temperature
data and follow the HRR. There appear to be a number of sensors where
the O2 and CO2 do not behave like I would expect.
I suggest that you first look at all the temperature data. If that is
not matching reasonably well, nothing else will. Next O2. Some of the
experimental measurements look reasonable, others I do not believe.
What is the difference between device G3 and G5 (Fig 16 and Fig 17)?
How can the model predict so well in one case and so badly in the
other? Fig 18 – why does the measured O2 concentration increase to
0.215 for approximately 100 s? Where are the uncertainty bounds on
these measurements? If you publish this work, you have to be able to
put uncertainty bounds on your measurements. Otherwise, how can you
assess the accuracy of the model?
What’s up with CO2 at G3 (Fig 10)? Do you believe the measurement?
Looks like noise to me. How about CO2 at G5 (Fig 12)? What happens at
200 s to make the CO2 concentration drop by 80%? I see no change in
the HRR at this point. Figure 9? What’s going on there? 16% CO2? Why
these sudden increases? Is someone smoking a cigarette near G2? Maybe
the forklift?
As far as your input file, CO_PRODUCTION=.TRUE. is not appropriate
here. This is just for under-ventilated compartment fires. I suggest
that you turn it off and just use the fixed yield. Even then, FDS
does not match CO data very well because it is very difficult to
predict the production rate. CO_PRODUCTION is an attempt to do it in
under-ventilated compartments. In your case, the fire is well-
ventilated and we just have to rely on an estimate of CO_YIELD.
Look at temperatures – the O2 and CO2 should follow the trend. If the
time trace does not qualitatively follow the FDS prediction, you need
to explain why the fire behavior so suddenly changed. Notice that all
the FDS plots rise with the HRR, steady out, and then decrease. If the
fire’s HRR is what is displayed, and nothing was done in the test lab
(like opening a door or whatever), then I would not trust either an O2
or CO2 measurement that does not follow the same trend as FDS. FDS may
over or under-predict the measurement, but typically it follows the
same trend.