&MESH IJK=14,92,8 XB=16,23,0,46,6,10/
Your overall domain is 10 m tall.
&TIME T_END=50.0 /
You are running your simulation for 50 s.
&SURF ID='fire', HRRPUA=6400, RAMP_Q='fireramp' /
&RAMP ID='fireramp', T=0.0, F=0.0/
&RAMP ID='fireramp', T=100, F=0.02941/
&VENT XB=19,19.707,22.5,23.207,0.1,0.1, SURF_ID='fire', COLOR='BLUE'/
At 50 s your fire is only 90 kW.
&DEVC XB=17,17,23,23,0.0,3, QUANTITY='LAYER HEIGHT',ID='smokeheight' /
&DEVC XB=17,17,23,23,0.0,3, QUANTITY='LOWER TEMPERATURE',ID='uptemp' /
&DEVC XB=17,17,23,23,0.0,3, QUANTITY='UPPER TEMPERATURE',ID='lotemp' /
You are telling FDS to compute the layer temperature for the first floor.
Do you expect that a fire that grows to 90 kW in 50 s will result in the upper layer descending from 10 m down to 3 m?