I would first determine whether the fire would have enough available oxygen by running a simple preliminary model with a 15MW fire with two 3m2 doors. I suspect that the fire would quickly become oxygen limited. This preliminary calculation would help you to determine the type of gas yield data that you should be looking for.
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+unsubscribe@googlegroups.com.
To post to this group, send email to fds...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/e1a1bb80-4b6b-4f60-80cc-4fbc8c833fed%40googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
To add to what Dave said, if you are confident in the HRR curve, the example 2-step mechanism used inhas shown very reasonable accuracy to CO prediction in both ventilated and under-ventilated full-scale compartments. There are validation metrics in the guide to check this.
On Sat, Jan 21, 2017 at 8:24 AM, Dave Sheppard <drdtsh...@gmail.com> wrote:
I would first determine whether the fire would have enough available oxygen by running a simple preliminary model with a 15MW fire with two 3m2 doors. I suspect that the fire would quickly become oxygen limited. This preliminary calculation would help you to determine the type of gas yield data that you should be looking for.
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To post to this group, send email to fds...@googlegroups.com.
To add to what Dave said, if you are confident in the HRR curve, the example 2-step mechanism used inhas shown very reasonable accuracy to CO prediction in both ventilated and under-ventilated full-scale compartments. There are validation metrics in the guide to check this.
On Sat, Jan 21, 2017 at 8:24 AM, Dave Sheppard <drdtsh...@gmail.com> wrote:
I would first determine whether the fire would have enough available oxygen by running a simple preliminary model with a 15MW fire with two 3m2 doors. I suspect that the fire would quickly become oxygen limited. This preliminary calculation would help you to determine the type of gas yield data that you should be looking for.
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To post to this group, send email to fds...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/10e49c3b-3d12-4a50-add1-e934d9f30326%40googlegroups.com.
For more options, visit https://groups.google.com/d/optout.