3D Smoke Rendering Not Representative of Actual Soot

231 views
Skip to first unread message

John William Bolduc

unread,
Nov 2, 2018, 7:52:57 PM11/2/18
to FDS and Smokeview Discussions
I ran the attached FDS file named "C783701_Wind_Test_13.txt" with FDS 6.7.0. This 120-second simulation is a fire (producing a lot of soot) in wind-tunnel type of test.

I feel that the results are representative of what should be expected, when I look at:
  • heat-release rate the hrr.csv file,
  • SmokeView renderings of SOOT/HRRPUV/C02  (sample image attached)
  • visibility devices located down-wind in my devc.csv file,
  • SmokeView renderings of a 10 m soot visibility isosurface (sample image attached)
However, I am surprised by what is shown in the SmokeView rendering for 3D Smoke (i.e. SOOT/TEMPERATURE/CO2).  You can have a look at the attached sample image.  The 3D Smoke images for this version of the model show a negligible amount of soot (even though I am convinced it has been modeled accurately).

In a previous run named "C783701_Wind_Test_10.txt" I had the same parameters, with only a 90-second duration.  In the 90-second version, SmokeView is showing a substantial amount of soot when I load the 3D Smoke (like expected).

In case it is a hardware limitation, I have attached a DxDiag.text file from my PC.  Please let me know if there is any other information that could help you troubleshoot, and thanks in advance.
C783701_Wind_Test_13.txt
C783701_Wind_Test_10_0100 - SOOT.png
DxDiag.txt
C783701_Wind_Test_13_devc.csv
C783701_Wind_Test_13_hrr.csv
C783701_Wind_Test_13_0100 - HRRPUV.png
C783701_Wind_Test_13_0100 - SOOT.png
C783701_Wind_Test_13_0005 - Soot Visibility ISOF at 10 m.png
C783701_Wind_Test_13.out
C783701_Wind_Test_10.txt
C783701_Wind_Test_10.out

Randy McDermott

unread,
Nov 3, 2018, 9:19:02 AM11/3/18
to FDS and Smokeview Discussions
I did a diff on your input files, and, as you said, I only see a difference in the time of the simulation.

One of the things that is new in the 6.7.0 bundle is a way to visualize CO2 and soot independently, colored by temperature---but this is only applicable to a special case.  The idea is being used for a new 2-step scheme for predicting in-flame CO and soot concentrations.  But the Smokeview labels for this, at the time of bundle release, were not (IMO) super clear, and I have been caught trying to visualize the wrong thing several times.  I think we will have this sorted out better in the next release.

In the mean time, for a 1-step reaction, you should only be looking at soot density and/or HRRPUV, as shown in the attached screen shot.  Please double check that this is the soot density your are loading and report back.  Thanks.


--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To post to this group, send email to fds...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/a70e103b-faff-400f-81a5-5edfb2437eed%40googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
Screen Shot 2018-11-03 at 9.09.11 AM.png

John William Bolduc

unread,
Nov 3, 2018, 5:02:26 PM11/3/18
to FDS and Smokeview Discussions
Hello Randy,

You are correct that I was not loading the "SOOT DENSITY", instead I had been loading the "SOOT/TEMPERATURE/CO2".

This tip has been helpful, because now when loading "SOOT DENSITY" I receive the attached error message that there are problems allocating memory for the 3D Smoke file.

Is this a hardware limitation for my PC and the amount of memory that can be allocated?


Regards,


John Bolduc
Error Allocating Memory for 3D Smoke.png

Glenn Forney

unread,
Nov 3, 2018, 6:51:21 PM11/3/18
to fds...@googlegroups.com
How much memory do you have? How big are your .s3d files?

Open then bounds dialog box, then open the time tab? Try skipping time frames

John William Bolduc

unread,
Nov 3, 2018, 7:53:50 PM11/3/18
to FDS and Smokeview Discussions
Hello Glenn,

You gave me a work-around for the memory allocation error I was having.  The "Time" tab under Dialogs >> Data bounds... allows me to load a limited duration of 3D Smoke rendering.  I can change the Data Loading "min time" / "max time" to something smaller than the entire duration of the model.  The only trick was that I needed to first load something smaller (like HRRPUV) before I can adjust the values for Data Loading.  After I first set the Data Loading to a smaller duration, I can then load the "SOOT DENSITY" without having a memory allocation error.

Thank you Glenn and Randy for your help.  That is all I need at this time.

To answer your questions Glenn, the attached screen-shot shows the size of my .s3d files.  Below is a summary of my PCs memory.

Processor: Intel(R) Core(TM) i7-7700 CPU @ 3.60GHz (8 CPUs), ~3.6GHz
Memory: 16384MB RAM
Available OS Memory: 16252MB RAM