Arvind, Palindra is correct, you have no walls at the site of the
vent. You have set your mesh boundaries at X=-2.0, Y=-0.5 and then
seem to have built a room from 0.0. The vent must either align with
the domain boundary or an object. If you want the 'floor area to
represent the room you either need the domain boundaries at the edges
of the floor or to create wall obstructions.
On Mar 6, 6:13 am, arvind tiwari <
arvindmit...@gmail.com> wrote:
> Dear FDS user's,
>
> I am finding error in Input file of FDS.It is showing the error "VENT
> 1 must be attached to a solid obstruction"
> Input file is also attached.