Hi people

Has anyone built a model for fire in a tank whose heat reaches another nearby tank?

Regards from Brazil

Jose Maria

Dave Sheppard

unread,
Jan 20, 2023, 7:41:51 AMJan 20
to FDS and Smokeview Discussions
If the fire was entirely inside the first tank, the heat transfer mechanisms to the second tank would be radiative and convective. I would just define the external temperature of the first tank and allow FDS to calculate the heat transfer to the other tank.

José Maria Pomarolli

unread,
Jan 30, 2023, 8:18:22 AMJan 30
to FDS and Smokeview Discussions
Tkank you very much

Jonathan Hodges

unread,
Jan 30, 2023, 9:40:52 AMJan 30
to FDS and Smokeview Discussions
Our analysis on large tank-to-tank fire spread indicated that additional validation was needed in this area. We compared the heat fluxes predicted by FDS to empirical correlations from the SFPE handbook (5th edition chapter 66 - Fire hazard calculations for large open hydrocarbon fires) and found we needed to adjust the PATH_LENGTH to improve agreement.