Flame length and flame height

313 views
Skip to first unread message

VIGNESHWARAN NARAYANAN PhD

unread,
Feb 11, 2021, 8:59:17 AM2/11/21
to fds...@googlegroups.com
Hello, 

Is there any easy way to measure flame length and flame height of a compartment fire? 

Can you please let me know?

Its excruciatingly time consuming process using smokeview 

Regards 
Vignesh 

ashutos...@gmail.com

unread,
Feb 11, 2021, 9:13:22 AM2/11/21
to FDS and Smokeview Discussions
Flame height is obtained as the extension till where the heat release rate is 99% of the total heat release rate of the fire. For doing that, HRRPUL, when integrated till the flame height should equal 99% of the total HRR. I have seen this being told in response to one of the earlier queries. Let us wait for other comments from learned members of FDS community.

VIGNESHWARAN NARAYANAN PhD

unread,
Feb 12, 2021, 1:48:24 AM2/12/21
to fds...@googlegroups.com
Thanks Ashutosh,

But my query is, How can we obtain flame height from FDS. Do we have a device that can do the purpose?. 

Have a good day
Thanks & Regards
Vigneshwaran Narayanan
Fire Researcher


--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/68d3c400-2cba-4214-8325-aab22c33f46cn%40googlegroups.com.

ASHUTOSH BHARTI

unread,
Feb 12, 2021, 1:54:16 AM2/12/21
to fds...@googlegroups.com
Yes. Place devices named "HRRPUL" along the flame extension.

VIGNESHWARAN NARAYANAN PhD

unread,
Feb 12, 2021, 3:43:16 AM2/12/21
to fds...@googlegroups.com
Thanks, But I believe to add this device one must be aware of flame length. In my case, I am not sure. How about using HRRPUV (as I know where to expect flames) and then use 99% fraction to determine flame effectiveness?

Have a good day
Thanks & Regards
Vigneshwaran Narayanan 
Fire Researcher

ASHUTOSH BHARTI

unread,
Feb 12, 2021, 4:00:10 AM2/12/21
to fds...@googlegroups.com
The flame length need not be known in advance. You can get HRRPUL at any number of points along the flame. Just try using DEVC XB=...,...,...,...,...,..., QUANTITY='HRRPUL', POINTS=...

VIGNESHWARAN NARAYANAN PhD

unread,
Feb 12, 2021, 7:44:57 AM2/12/21
to fds...@googlegroups.com
Thanks. I also happen to find another method where HRRPUV was mentioned with 95%-97% of HRR is considered as Flame lengths

Have a good day
Thanks & Regards
Vigneshwaran Narayanan PhD
Fire Researcher