Dear everyone,
Currently, I am doing a simulation about one office. The fire source is put at the office on the far left. When I ran the simulation, I noticed that the office's temperature on the far right was higher than the office in the middle. May I know what the reasons are cause this error?
Best regards,
Wong Yeng Chiang
Wong Yeng Chiang
unread,
Oct 24, 2021, 10:37:12 AM10/24/21
Reply to author
Sign in to reply to author
Forward
Sign in to forward
Delete
You do not have permission to delete messages in this group
Copy link
Report message
Show original message
Either email addresses are anonymous for this group or you need the view member email addresses permission to view the original message
to FDS and Smokeview Discussions
Dear everyone,
Is the temperature distribution normal and correct?
Best regards,
Wong Yeng Chiang
Kevin McGrattan
unread,
Oct 24, 2021, 11:00:33 AM10/24/21
Reply to author
Sign in to reply to author
Forward
Sign in to forward
Delete
You do not have permission to delete messages in this group
Copy link
Report message
Show original message
Either email addresses are anonymous for this group or you need the view member email addresses permission to view the original message
to fds...@googlegroups.com
It is not possible for anyone to say whether this is "normal and correct". Fire modeling does not work that way.