Firstly, you should define the maximum fire size.
Secondly, you should have the designed fire growth rate (ultrafast,
fast, medium or slow).
Thirdly, put those parameter into calculation: Q = at^2, Q is the max.
fire size; a is the fire growth constant; t is the time at which Q is
max.
For example you want to define a fire of 2MW, fast fire.
a = 0.0469kW/t^2
Q = 2000kW
t = 206.5s
HRRPUA = 250kW/m^2
In FDS, you should write:
&SURF ID='FIRE', HRRPUA=250.0, TAU_Q=-206.5, COLOR='RED' /
&OBST XB=0,2,0,4,0,1, SURF_IDS='FIRE' /
Now you have a 2m x 4m object which top surface will burn as a t
square fire to 2MW and then keep constant.