Quadratic increasing HRR.

473 views
Skip to first unread message

Daan

unread,
May 27, 2008, 4:24:44 PM5/27/08
to FDS and Smokeview Discussions
I'm trying to simulate a train fire using a specified fire curve. Part
of the curve is quadratic and I would like to define this in the
model. According to section 8.5 of the User Manual it is possible to
create a quadratic increasing HRR when TAU is set negative. When I set
up a simple model and set the TAU at -1 the HRR doesen't increase as I
aspected (it also doesn't remain constant after 10 seconds as the
manual states).

The ramp is defined as follows:
&SURF ID='BURNER', HRRPUA=100.0, PART_ID='smoke', COLOR='RED',
RAMP_Q='BURNRATE'/
&RAMP ID='BURNRATE', T=0000.0, F=0.0 /
&RAMP ID='BURNRATE', T=0010.0, F=-1.0 /

Hopefully someone can help me with this problem.

Sincerely yours,
Daan

dr_jfloyd

unread,
May 27, 2008, 4:28:20 PM5/27/08
to FDS and Smokeview Discussions
The RAMP applies to the HRRPUA not the TAU

Antony

unread,
May 28, 2008, 8:42:37 PM5/28/08
to FDS and Smokeview Discussions
Firstly, you should define the maximum fire size.
Secondly, you should have the designed fire growth rate (ultrafast,
fast, medium or slow).
Thirdly, put those parameter into calculation: Q = at^2, Q is the max.
fire size; a is the fire growth constant; t is the time at which Q is
max.

For example you want to define a fire of 2MW, fast fire.
a = 0.0469kW/t^2
Q = 2000kW
t = 206.5s
HRRPUA = 250kW/m^2

In FDS, you should write:
&SURF ID='FIRE', HRRPUA=250.0, TAU_Q=-206.5, COLOR='RED' /
&OBST XB=0,2,0,4,0,1, SURF_IDS='FIRE' /

Now you have a 2m x 4m object which top surface will burn as a t
square fire to 2MW and then keep constant.

Antony

unread,
May 28, 2008, 8:45:00 PM5/28/08
to FDS and Smokeview Discussions
The above command should be written:

&OBST XB=0,2,0,4,0,1, SURF_IDS='FIRE','INERT','INERT' /

Now you have a 2m x 4m object which top surface will burn as a t-
square fire up to 2MW and then keep constant. The side surfaces and
bottom surface will not burn.

Daan

unread,
Jun 1, 2008, 12:04:02 PM6/1/08
to FDS and Smokeview Discussions
Thank you very much! After all it wasn't as hard as I tought it would
be.

But probably you can help me with the next issue. after the quadratic
increasing fire it is constant for a while and than decreases lineary
to zero. Can I combine a quadratic increasing HRR with a lineary
decreasing HRR?

Daan

Kevin

unread,
Jun 1, 2008, 3:09:16 PM6/1/08
to FDS and Smokeview Discussions
Use RAMP_Q and do whatever you want.