[Deposition] Page
1022
Q. 0.13 [gpm/SF]. In connection with your
investigation, did you determine what density would be required to control the
fire with a 50 foot clearance involving two stacked pallets high?
A. No.
Q. Is that
possible to calculate?
A. Presumably you
could change the parameters of the calculation to seek out the density at which
control was achieved.
Q. Based upon
your model, does the heat release under your scenario with the 50 foot clearance
and a 0.45 [gpm/SF] density increase over time?
A. The heat release increases over
time.
Q. Does it ever decrease at any point?
A. Not during the
simulation as I - - Well, let me check. I remember it’s - - it stopped
growing so fast, but I’m - - at the ten minute mark its rate of growth is
slowing, but it is continuing to grow.
Q. Would you point out where you are referring to in the
report for that information.
A. Figure 17 on page 68.
Q. If you carry those lines out, do you ever reach a
point where the heat release level off?
A. Do I believe it would if the calculation had
continued? Is that the question?
Q. Yes. That’s correct. All right. Go
ahead.
A. At the ten
minute mark on the simulation, the number of heads activated is right about at
the design area, 2,500 square feet. We’ve got - - if you look at
Figure 18, we have I think it’s 33 heads
operating at that time. And that’s basically 2,500 square foot of
area where sprinklers are operating, which is the design area. And it
would be my judgment since the fire is
continuing to grow, though at a reduced rate, that I would expect the
fire not to be - - if you don’t contain it by the time you reached the design
area, you’re not - - you won’t.
Q. Right. But the amount of heat release gradually
levels off at some point, does it not, based upon the amount of fuel that you
have available to burn? I mean it’s not going - -
A. Yeah. If we’re talking about will you ultimately
get to a peak, I mean all fires, you know, die out at some point, yes. I
mean they grow to a size, they burn, they die out.
Q. Okay.
A. And I guess all I’m saying here is that since we have
a fire that continues to grow at a reduced rate, certainly not continuing to
escalate, it would be my - - my judgment that since the fire is still growing at
the design area, you know, the number of heads consistent with the design area,
that this fire won’t be controlled and the - - you know, we’ll get right over,
you know, a large area such that control will not have occurred.
Q. Would you
agree with me that under the scenario you modeled with two pallet high that the
sprinkler system does have some effect on the increase in the heat release over
time?
A. Yes, it does.
Q. And would you
agree with me that the dynamics of the fire that occurs as you modeled it with
the two pallet high is significantly different than the dynamics for the fire
that you modeled with three racks high?
A. Yes, there’s
“significantly” in two regards. One is that since the three tier
represents a more severe challenge, its heat release rates are inherently
larger.
Q. Okay.
A. And secondly,
you know, it is the case that the pallets stacked, one, you see a change - - you
see a reduction in the rate of growth which is not at all apparent in the three
tier Class II in Figure 10.