Dear ALL,
1) In the user guide, it is 3 for reflecting signs (default value used in FDS) and 8 for light emitting signs.
2) A visibility of 10m is generally adopted as one of the tenability criteria in FDS simulation.
3)Annex B of NFPA 130 says: "B.2.1.3 Smoke Obscuration Levels. Smoke obscuration levels should be continuously maintained below the point at which a sign internally Illuminated at 80 lx (7.5 ft-candles) is discernible at 30 m (100 ft) and doors and walls are discernible at 10 m (33 ft)."
My doubts are as follows:
1) If we use light emitting exit sign in a building, is it well reasonable to take 8 for VISIBILITY_FACTOR in FDS? As visibility depends on many factors, e.g. illumination in the room, how do you consider these factors in your FDS?
2) as 10m visibility is generally accepted, but If the exits sign is more than 10m, then it is still impossible to recognize the way of evacuation(EXIST SIGNS) even we keep a visibility of 10m in the enclose. What is your understanding for the 10m visibility? Is it to help evacuees to easily identify the surrounding obstacles during moving ahead, or to identify the way of evacuation (i.e. see the exits signs)? If the former, the background for calculating the visibility should be surrounding obstacles other than the exits sign? Is it correct?
3) What is your suggestion for general value for the factor?
Lin P.
Fire engineer