Heat release rate per unit volume(HRRPUV)

226 views
Skip to first unread message

pc_huang

unread,
Mar 12, 2021, 8:41:01 PM3/12/21
to FDS and Smokeview Discussions
Hello, everyone. The pictures below are contents about heat release rate in FDS_Technical_Reference_Guide for FDS 6.3.0 and FDS 6.2.0 respectively. I want to ask why upper bound on the local HRRPUV is abandoned in the new edition?   1.png2.png

Randy McDermott

unread,
Mar 12, 2021, 8:44:12 PM3/12/21
to FDS and Smokeview Discussions
Because we found from the UMD_Line_Burner validation case that we had errors in the flame temperature of about 200 C.

On Fri, Mar 12, 2021 at 8:41 PM pc_huang <25317...@qq.com> wrote:
Hello, everyone. The pictures below are contents about heat release rate in FDS_Technical_Reference_Guide for FDS 6.3.0 and FDS 6.2.0 respectively. I want to ask why upper bound on the local HRRPUV is abandoned in the new edition?   1.png2.png

--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/9cc85b41-1eae-4d90-b5c8-df8981a4ea10n%40googlegroups.com.
Reply all
Reply to author
Forward
0 new messages