We have a similar requirement embodied in C/VM2 here is New Zealand. The purpose of this metric is for occupant egress. The direction is UP. The locations are on egress routes, often just one at the point of closest proximity to the design fire in the compartment of fire origin. Where there is more than one escape route the metric is redundant as occupants will not move into smoke and heat (Purser et al. on human behaviour in fires).
There are also times when one might want to assess emergency responder FED thermal hazards. The threshold increases due to PPE. The location should be rationalized based on anticipate response (research FBIM – Fire Brigade Intervention Model).
t.
--
You received this message because you are subscribed to a topic in the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/fds-smv/C9y44pD7758/unsubscribe.
To unsubscribe from this group and all its topics, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/8d8cd5ac-11d6-4c84-8141-8c0a0b37a666n%40googlegroups.com.
I suspect that you need to understand the concept of Fractional Effective Dose (FED). The effects of heat on people are cumulative, but simultaneously decay over time. In occupant egress people are moving along a path a defined rate. So the FED is calculated over the travel path where the radiation from the hot layer above varies in time and space.
Dr Floyd’s comment is also correct. If an occupant were to stand still at the point of maximum received radiation flux from above on the egress path for the total evacuation time and not be incapacitated, then thermal radiation should not prevent evacuation under the fire scenario.
Note that many codes do not require FED thermal, but have a go/no go maximum heat flux (often expressed as upper layer temperature).
From: fds...@googlegroups.com [mailto:fds...@googlegroups.com] On Behalf Of mst-parkhachev
Sent: Sunday, 17 March 2024 9:01 PM
To: FDS and Smokeview Discussions
Subject: [fds-smv] Re: tenability and choice of the device
Is this true? Isn't the flow averaged in all directions when calculating the integated intensity?
--
You received this message because you are subscribed to a topic in the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this topic, visit https://groups.google.com/d/topic/fds-smv/C9y44pD7758/unsubscribe.
To unsubscribe from this group and all its topics, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/12bf9b7a-d6eb-409d-a985-145acf27eaedn%40googlegroups.com.
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/2f5d2d9d-dfdf-4ea5-8728-3bf6fb555963n%40googlegroups.com.
See Dr Floyd’s early comment. FED thermal at the point of maximum received radiation flux (in the compartment of fire origin) should be higher than the FED thermal calculated along an egress path over travel time. So for a fire safety design the point measure will be conservative as it should fail tenability criteria earlier.
You should justify your preferred method, and you might want to talk with your regulator or examine the Code that you are interested in as this measurement is often prescribed.