Der FDS User,
I am working on a fire modeling in a closed hall/ space and based on the FDS user guide for the closed compartment I added the pressure zone in the compartment. After adding the pressure zones I found that the hrr is continuously increasing.
To test the accuracy of the model I started the simulation where I opened the door leading to the closed hall and provided the open vent at the end of the domain, Case number 1. See the attached image. In that case, I found the HRR as per the defined value in the model.
While for the actually closed compartment scenario, I tested two cases depending upon the location of the pressure zone. Case 2 defines the pressure zone outside the fire origin zone and Case 3 pressure zone within the fire origin zone. See the attached image. In these two cases hrr continuously increase with time event with fixed HRRPUA value defined in the model.
The mechanical system are as follows
a) Extract = 20 m3/s
b) Supply = 19 m3/s (95%)
Please let us know your thought on how to model such a closed scenario.
Thanks for your time and suggestions.
Regards
Wali
Dear Jason,
I
followed one local_leakage temperature fds example, where the supply vent is
applied at one side along with the top and bottom leakage phenomenan are
observed with the open boundary at the other end of the domain.
Next,
based on you suggestion I updated the model where I defined the pressure zone
inside the fire compartment and also remove the open vent from the model but
keep the door leakage surface. After performing the simulation still i am
getting a same results i.e increase in hrr with time. I considered two cases,
see attached images and relevatent fds files.
Please
have a look and advice.
Regards
Wali
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/c1311173-35fc-48d6-b6d2-253875c9005bn%40googlegroups.com.