Since the author applied the 'DIESEL' surface to all sides of the
OBST, the total exposed surface area is 1.872 m^2 (assuming the bottom
is not exposed with a min_X value of 0.
With the HRRPUA of 750 the total HRR would be about 1404 kW, and based
on the comment at the top of 'Max heat release rate: 0.75 MW', I think
this was an error in the HRRPUA value. It should be closer to
HRRPUA=400.641 for this surface area.
If all the author wants is 0.75 MW released from the top surface of
the OBST, then the &OBST line needs to change from SURF_ID='DIESEL
POOL' / to something like SURF_IDS='DIESEL POOL','INERT','INERT' /
This would make the total surface area for the top of the OBST at 1.56
m^2.
Which would mean the 'DIESEL POOL' HRRPUA should then be set at
480.769 kW to get a total HRR of 0.75 MW.
It would be a nice feature to just set the desired HRR value and let
the model calculate the total area of the SURF it is applied to and
then set a HRRPUA value internally to whatever it needs to be to
create the expected results. But, until then, you are correct, the
surface area has to be calculated first and used to determine the
HRRPUA value.